Default Home ac help

I have an issue with my home ac. I was wondering what these two components are called. They are in the condenser unit.



Sent from my SAMSUNG-SM-G890A using Tapatalk
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-09-2019, 07:39 PM   #2
LonestarGent
Six Point
 
LonestarGent's Avatar
 
Join Date: Dec 2015
Location: Hutto
Hunt In: Grayson, Young, Williamson
Default

Relay and reversing valve. Is it stuck in heat mode?

Sent from my SM-G950U using Tapatalk
LonestarGent is offline   Reply With Quote Back To The Top
Old 04-09-2019, 07:48 PM   #3
bowhntrmatt
Pope & Young
 
bowhntrmatt's Avatar
 
Join Date: Dec 2009
Location: Stockdale
Hunt In: Concho, Val Verde
Default

Quote:
Originally Posted by LonestarGent View Post
Relay and reversing valve. Is it stuck in heat mode?

Sent from my SM-G950U using Tapatalk
Yep.

Not very often you see that type of relay in a condenser. Maybe a less-zoomed pic? Maybe a mcguyver job if not a really old unit.
bowhntrmatt is offline   Reply With Quote Back To The Top
Old 04-09-2019, 08:03 PM   #4
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

Less zoomed in.

Sent from my SAMSUNG-SM-G890A using Tapatalk
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-09-2019, 08:04 PM   #5
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

This is a unit from the 80s. The fan and the condenser do not turn on. I have 220 to the unit, the capacitor has been tested and is good. I replace the contactor and the fan motor. I replace the fan motor just because the bearings were going out last time I used it. When I turn the unit on, I do not get the 24 volts to the contactor which would Supply voltage to the compressor and fan motor. What sends 24 volts to the contactor?

Last edited by stinkbelly; 04-09-2019 at 08:08 PM.
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-09-2019, 08:48 PM   #6
LonestarGent
Six Point
 
LonestarGent's Avatar
 
Join Date: Dec 2015
Location: Hutto
Hunt In: Grayson, Young, Williamson
Default

Quote:
Originally Posted by stinkbelly View Post
This is a unit from the 80s. The fan and the condenser do not turn on. I have 220 to the unit, the capacitor has been tested and is good. I replace the contactor and the fan motor. I replace the fan motor just because the bearings were going out last time I used it. When I turn the unit on, I do not get the 24 volts to the contactor which would Supply voltage to the compressor and fan motor. What sends 24 volts to the contactor?
Transformer in the air handler but need to confirm the call from the stat.

Sent from my SM-G950U using Tapatalk
LonestarGent is offline   Reply With Quote Back To The Top
Old 04-09-2019, 08:55 PM   #7
double bogey
Ten Point
 
Join Date: Oct 2015
Location: Mesquite
Hunt In: where ever I can
Default

Does it have a wiring diagram you could take a pic of? Unit could have pressure switches or temp switches Keeping it off.

Most older residential units don't have much in the way of pressure and temp limit switches on them. But there are always exceptions, typically on deluxe models. the relay is most likely a defrost relay. On newer units it will be mounted on the circuit board.

Dadgummit my typing skills suck tonight, must be the narcotics. I mistype at least one letter per sentence.
double bogey is offline   Reply With Quote Back To The Top
Old 04-09-2019, 09:33 PM   #8
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

I was told if the air handler blows, then the transformer is good. Is that correct?

I will get a diagram tomorrow. I don't like snakes in the dark.
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-09-2019, 10:24 PM   #9
txoutdoorsman24
Pope & Young
 
txoutdoorsman24's Avatar
 
Join Date: Oct 2010
Location: San Antonio
Hunt In: In camo
Default

If you’re not getting 24 to the contactor, then the problem is either the Tstat or control board in the indoor unit. Possibly the transformer.

Easiest way to tell if the outdoor unit components work is just press in the contactor and see if everything comes on. That will tell you the problem is inside the house for sure.

Does the inside unit come on? Turn on the Fan on the tstat and see what happens. No fan, means either tstat, Control board or transformer is bad.

Last edited by txoutdoorsman24; 04-09-2019 at 10:27 PM.
txoutdoorsman24 is offline   Reply With Quote Back To The Top
Old 04-09-2019, 11:47 PM   #10
double bogey
Ten Point
 
Join Date: Oct 2015
Location: Mesquite
Hunt In: where ever I can
Default

Pushing in the contactor will only tell you if the compressor and fan are capable of running or not. This being a heat pump it is somewhat more complicated than a straight ac unit. That's why I asked for a wiring diagram, to assist with troubleshooting. You could have as many as 8 low voltage control wires coming into this unit. A voltmeter and the ability to use it will be required.
double bogey is offline   Reply With Quote Back To The Top
Old 04-10-2019, 06:29 AM   #11
twistedmidnite
Ten Point
 
twistedmidnite's Avatar
 
Join Date: Jun 2009
Location: Gilmer, TX
Hunt In: texas
Default

Pull inside cover and check 3 amp fuse first. Also verify that you are getting power to the inside unit.
twistedmidnite is online now   Reply With Quote Back To The Top
Old 04-10-2019, 06:43 AM   #12
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

Here is the diagram from the unit.

Sent from my SAMSUNG-SM-G890A using Tapatalk
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-10-2019, 07:07 AM   #13
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

When I turn the thermostat to Cool and set the temperature below the current temperature the blower in the house will turn on and it will blow air. Nothing happens on the outside of the house.

This is a heat pump as stated earlier. Around Christmas it sounded like the bearing in the fan motor in the outside unit were starting to go bad. I decided to turn the unit to electric element heating and replace the motor later. I forgot and when I decided to turn the AC on this year it would do nothing. That is how I got to where I am now. I knew I needed a new fan motor. I decided to replace the contactor because it is original. I had the capacitor tested by the electric motor shop that sells motors and they said it was good.

I was told that if the inside blower fan is blowing it isn't a problem with the transformer. I don't know if that is correct or not.

I didn't see the 3amp fuse referenced above. Where should I look for that?

I put new batteries in the thermostat just to be safe.
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-10-2019, 07:32 AM   #14
eradicator
Pope & Young
 
eradicator's Avatar
 
Join Date: Feb 2007
Location: Arlington,TX/Pecos County
Default

Freon leak and automatic shut-off?
eradicator is offline   Reply With Quote Back To The Top
Old 04-10-2019, 09:00 AM   #15
txoutdoorsman24
Pope & Young
 
txoutdoorsman24's Avatar
 
Join Date: Oct 2010
Location: San Antonio
Hunt In: In camo
Default

Quote:
Originally Posted by stinkbelly View Post
When I turn the thermostat to Cool and set the temperature below the current temperature the blower in the house will turn on and it will blow air. Nothing happens on the outside of the house.

This is a heat pump as stated earlier. Around Christmas it sounded like the bearing in the fan motor in the outside unit were starting to go bad. I decided to turn the unit to electric element heating and replace the motor later. I forgot and when I decided to turn the AC on this year it would do nothing. That is how I got to where I am now. I knew I needed a new fan motor. I decided to replace the contactor because it is original. I had the capacitor tested by the electric motor shop that sells motors and they said it was good.

I was told that if the inside blower fan is blowing it isn't a problem with the transformer. I don't know if that is correct or not.

I didn't see the 3amp fuse referenced above. Where should I look for that?

I put new batteries in the thermostat just to be safe.
Does the contactor close on the call for cool?
txoutdoorsman24 is offline   Reply With Quote Back To The Top
Old 04-10-2019, 09:27 AM   #16
twistedmidnite
Ten Point
 
twistedmidnite's Avatar
 
Join Date: Jun 2009
Location: Gilmer, TX
Hunt In: texas
Default

There's a fuse in there, different locations on different unit's. I'f it's blown the board won't have power. You said Tou used the emergency electric heat. Occasionally my unit will pop the fuse if we accidentally switch the thermostat to electric heat. Kill all power and pull the cover and poke around for the fuse.
If you have everything on and push the 24v connector outside does the outside unit come on?
twistedmidnite is online now   Reply With Quote Back To The Top
Old 04-10-2019, 09:57 AM   #17
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

When I turn on the AC, I will get 220 V to the contactor, but no power through the contactor.

Txoutdoorsman24, I am not sure what you mean by push the 24v connector. I don't see a place to push the contactor to allow 220 V to pass through it if that is what you mean.

When I push the button in the middle of the relay of the first picture, the reversing valve clicks like it is turning on.

I think I need to look for a fuse and I need to check the transformer to see if it is putting out 24V.
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-10-2019, 10:03 AM   #18
barnett77859
Ten Point
 
barnett77859's Avatar
 
Join Date: Oct 2006
Location: Elliott
Hunt In: Elliott
Default

you may have a high head pressure safty on the out side unit that is resettable
or you could have a low voltage wire broken that come from the inside unit or t stat
barnett77859 is offline   Reply With Quote Back To The Top
Old 04-10-2019, 12:47 PM   #19
HogHunter34
Ten Point
 
HogHunter34's Avatar
 
Join Date: Nov 2008
Location: Whitehouse, Tx
Hunt In: Anderson County
Default

Maybe 24v coil on contactor is no good?
HogHunter34 is online now   Reply With Quote Back To The Top
Old 04-10-2019, 01:24 PM   #20
Smith
Four Point
 
Join Date: Aug 2012
Location: Dripping Springs
Hunt In: TX Hill Country and Panhandle
Default

If you take those little screws out on the black cover on the contractor you will be able to push the contacts in and the unit should start. Sounds like your issue is the 24v coming to the contractor.
Smith is offline   Reply With Quote Back To The Top
Old 04-10-2019, 03:51 PM   #21
txoutdoorsman24
Pope & Young
 
txoutdoorsman24's Avatar
 
Join Date: Oct 2010
Location: San Antonio
Hunt In: In camo
Default

Quote:
Originally Posted by stinkbelly View Post
When I turn on the AC, I will get 220 V to the contactor, but no power through the contactor.

Txoutdoorsman24, I am not sure what you mean by push the 24v connector. I don't see a place to push the contactor to allow 220 V to pass through it if that is what you mean.

When I push the button in the middle of the relay of the first picture, the reversing valve clicks like it is turning on.

I think I need to look for a fuse and I need to check the transformer to see if it is putting out 24V.
On the contactor, there is a flat plastic cap over the contacts themselves. Remove the two small Phillips head screws and you can push in the contactor pads.
Your relay is good sounds like. You could have ants, a spider, or lizards or some kind of insect in the contactor. That was a common problem for outside units not coming on. if not, the issue is coming from inside most likely.

Last edited by txoutdoorsman24; 04-10-2019 at 03:53 PM.
txoutdoorsman24 is offline   Reply With Quote Back To The Top
Old 04-10-2019, 03:55 PM   #22
double bogey
Ten Point
 
Join Date: Oct 2015
Location: Mesquite
Hunt In: where ever I can
Default

Your diagram shows a low pressure switch. If the refrigerant pressure is lower than the setting on this switch, nothing will run outside. Do you have a voltmeter? We can take a couple of readings and see what the problem is. Send me a pm
double bogey is offline   Reply With Quote Back To The Top
Old 04-10-2019, 07:27 PM   #23
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

I just got out of the attic. It is hot up there. I found two issues. One of the wires coming from the 24v side of the Transformer touched the back of the heating element and was welded to it. It burned through the insulation. Also on the 240-volt side of the Transformer the common contact appears to be rigged and it just fell out when I touched it. I obviously need a new Transformer. I'm not exactly sure which one to get there's not all the writing on it like I expected. This is for a heat pump and it has a serial number with the last part of it 35a. I don't know if that means anything or not.

Sent from my SAMSUNG-SM-G890A using Tapatalk
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-10-2019, 07:30 PM   #24
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

Transformer pics

Sent from my SAMSUNG-SM-G890A using Tapatalk
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-10-2019, 07:58 PM   #25
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

I found it on Repair Clinic. It's a 208 or 240 volts to 24 volts transformer with a rating of 40 VA. Now I need to just find one
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-10-2019, 08:29 PM   #26
double bogey
Ten Point
 
Join Date: Oct 2015
Location: Mesquite
Hunt In: where ever I can
Default

Got a grainger nearby?
any 208-240 x 24v 40va will work if it will mount. If you have a short somewhere, it could cause your transformer issues. Check your control wires outside for damage from pets or rodents. dogs like to chew on them for some reason.
double bogey is offline   Reply With Quote Back To The Top
Old 04-15-2019, 01:42 PM   #27
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

I installed the transformer and I am still not getting 24v to the contactor at the condenser. I am kind of thinking it might be the time delay switches or the thermostat. I couldn't find a heat pump compatible thermostat locally.

When it was working, I would turn the system on and I would hear a click at the thermostat. I would then hear what sounded like water running and then about 30 seconds later the fan blower would turn on. Now I turn the system on, I hear the click, 30 seconds or so later the fan blower turns on. So I am missing the step where the compressor turns on which make me think one of the time delay switches is bad.
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-15-2019, 01:46 PM   #28
txoutdoorsman24
Pope & Young
 
txoutdoorsman24's Avatar
 
Join Date: Oct 2010
Location: San Antonio
Hunt In: In camo
Default

Did you ever get to look at the contactor and make sure it's good, nothing stuck in it?

Can you get to the wire terminals o nthe Tstat? If so, pull the face off and check to see it you have 24 to the red wire and Common, R terminal and C terminal. you have batteries in the thermostat right?
txoutdoorsman24 is offline   Reply With Quote Back To The Top
Old 04-15-2019, 03:07 PM   #29
bowhntrmatt
Pope & Young
 
bowhntrmatt's Avatar
 
Join Date: Dec 2009
Location: Stockdale
Hunt In: Concho, Val Verde
Default

Turn Tstat to cool.

Does the blower inside come on, and not the outside unit, or nothing at all?

If nothing at all, you still have a low voltage issue of some sort.

If inside does come on, check for 24v across y and c where it comes into the outdoor unit (usually wire nutted right inside the unit). If you are getting 24v, your problem is likely a pressure switch or relay. If not, go back inside and trace back to where you are losing your 24v call.
bowhntrmatt is offline   Reply With Quote Back To The Top
Old 04-15-2019, 09:05 PM   #30
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

I installed a new contactor first.

When I turn the system to cool the blower comes on, but not anything outside.

The electric heater works, but not the heat pump because once again the condenser will not turn on.

I can get to the terminals in the thermostat. Does it need to have 24 volts with the unit off or in cool or does it matter?

While looking around inside the condenser I found this switch. Where does it go and how does it work? I assume it's a thermal switch.



Sent from my SAMSUNG-SM-G890A using Tapatalk
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-15-2019, 09:08 PM   #31
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

Yes batteries in the thermostat

Sent from my SAMSUNG-SM-G890A using Tapatalk
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-15-2019, 09:14 PM   #32
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

Here are the terminals in the thermostat. I do not have any wires in the W3, B, or L position.

Sent from my SAMSUNG-SM-G890A using Tapatalk
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-15-2019, 11:15 PM   #33
txoutdoorsman24
Pope & Young
 
txoutdoorsman24's Avatar
 
Join Date: Oct 2010
Location: San Antonio
Hunt In: In camo
Default

You shouldn’t have any in those terminals. That looks fine.

You might be able to get 24v on the R terminal and that mounting screw below. You don’t have a common terminal in that Tstat. It’s getting hard to diagnose now that obvious is out of the way.
With a call for cool, blower comes on but nothing outside. I’d go to the outdoor unit and make sure no Tstat wires were chewed up by rodents and such. Tstat seems to be good. Issue has to be in the wiring or a relay. Might be on a control board.

How long ago did you replace that contactor?
txoutdoorsman24 is offline   Reply With Quote Back To The Top
Old 04-16-2019, 03:09 AM   #34
Uncle Saggy
Pope & Young
 
Uncle Saggy's Avatar
 
Join Date: May 2009
Default

My advice is not to pay attention to what some are saying.
If you are unfamiliar with the electrical components in the unit DO NOT remove the cover and press to test. Thatís stupid advice

Also, if 24v to the contractor is interrupted due to a system safety being open, itís to prevent damage to the system and manually pushing the contacts bypasses the safety. More stupid advice
Uncle Saggy is offline   Reply With Quote Back To The Top
Old 04-16-2019, 04:00 AM   #35
be12hunt
Ten Point
 
be12hunt's Avatar
 
Join Date: Jan 2015
Location: Lake Jackson, TX
Hunt In: Montell, TX
Default

Is it possible you have a drain pan float switch inside? That would kill 24v to condenser but still let inside come on.
be12hunt is offline   Reply With Quote Back To The Top
Old 04-16-2019, 06:37 AM   #36
ofishil
Ten Point
 
ofishil's Avatar
 
Join Date: Feb 2009
Location: Corpus
Default

Im not sure of terminology but on mine last year the wire that goes from outside unit to inside was broken inside the wire insulation. I tried for a few days in the heat of summer and 2 different ac guys. I finally was going to repull that wire and I was pulling on it and it came apart. It was like finding gold for me.
ofishil is offline   Reply With Quote Back To The Top
Old 04-16-2019, 07:11 AM   #37
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

The contactor was replaced a week or so ago when this all started.

I don't have any drain pan float switch. This is an OLD unit.

I will check the wires tonight. My first thought was the wires, but they looked good. I will look harder.

The switch I found yesterday is the heat pump defrost thermostat/switch. Would that be the issue? It was just hanging down along the side of the compressor.

Last edited by stinkbelly; 04-16-2019 at 07:31 AM.
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-16-2019, 09:58 AM   #38
ofishil
Ten Point
 
ofishil's Avatar
 
Join Date: Feb 2009
Location: Corpus
Default

I think this is the video I watched.

ofishil is offline   Reply With Quote Back To The Top
Old 04-16-2019, 04:02 PM   #39
bowhntrmatt
Pope & Young
 
bowhntrmatt's Avatar
 
Join Date: Dec 2009
Location: Stockdale
Hunt In: Concho, Val Verde
Default

If your indoor unit will come on, you are definitely getting 24v.

Have you checked to see if you are getting 24v on Y wire outside during a call for cooling?

That defrost thermostat should be attached to the outdoor coil via a little metal clip. On a unit this old, it probably rusted off. It wont affect the unit coming on in cooling mode.

Might be time to call in an expert. Only so much diagnosing can be done over the web.

That old unit costs you money every time it turns on. Consider that before investing too much more time or $$.
bowhntrmatt is offline   Reply With Quote Back To The Top
Old 04-16-2019, 10:12 PM   #40
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

I am getting 24 volt power to the yellow red and orange out in the condenser when the thermostat is set to cool. I only get it to the red when the thermostat is turned to off. The yellow goes through a low pressure switch and I get no power on the other side of it. It looks like the thermostat is working in all settings. Here is a picture of the low pressure switch. I'm not sure if it's supposed to be open or closed.

Sent from my SAMSUNG-SM-G890A using Tapatalk
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-16-2019, 10:36 PM   #41
bowtecmike
Ten Point
 
bowtecmike's Avatar
 
Join Date: Jun 2009
Location: Shallowater,tx
Hunt In: Kent County, SA St Park
Default

Bypass that low pressure switch. If nothing else it will eliminate that possibility. It's normally closed, so cut and wire nut together. You can put it back in series easily.

pray for rain
bowtecmike is offline   Reply With Quote Back To The Top
Old 04-16-2019, 10:43 PM   #42
bowtecmike
Ten Point
 
bowtecmike's Avatar
 
Join Date: Jun 2009
Location: Shallowater,tx
Hunt In: Kent County, SA St Park
Default

The switch that was hanging down usually has a small metal clip and it goes on the liquid line, it is not the issue right now.

pray for rain
bowtecmike is offline   Reply With Quote Back To The Top
Old 04-17-2019, 07:02 AM   #43
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

This is an old unit. The one hanging down was actually glued on. The newer version of it has the clip.

Thanks
stinkbelly is offline   Reply With Quote Back To The Top
Old 04-17-2019, 07:29 AM   #44
bowhntrmatt
Pope & Young
 
bowhntrmatt's Avatar
 
Join Date: Dec 2009
Location: Stockdale
Hunt In: Concho, Val Verde
Default

Do you have gauges?

Sounds like a refrigerant problem if the lps is open.
bowhntrmatt is offline   Reply With Quote Back To The Top
Old 04-17-2019, 08:35 AM   #45
Mayhem
Pope & Young
 
Mayhem's Avatar
 
Join Date: Oct 2006
Location: porter, tx
Hunt In: crockett, county
Default

Sounds like you need to call a professional.
Mayhem is offline   Reply With Quote Back To The Top
Old 04-17-2019, 08:54 AM   #46
Smith
Four Point
 
Join Date: Aug 2012
Location: Dripping Springs
Hunt In: TX Hill Country and Panhandle
Default

The pressure switch is supposed to be closed. If itís open itís because of low pressure.
Smith is offline   Reply With Quote Back To The Top
Old 04-17-2019, 09:00 AM   #47
stinkbelly
Pope & Young
 
stinkbelly's Avatar
 
Join Date: Feb 2009
Location: Weatherford
Default

I don't have gauges.

I have learned more in the past 2 weeks about my unit than I have in the previous 20 years of living here.
stinkbelly is offline   Reply With Quote Back To The Top
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:58 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2019, vBulletin Solutions Inc.
Copyright 1999-2012, TexasBowhunter.com