    Rv electric plug question

    Got on a lease and need to move the plug about 80 ft. I'm gonna pit a junction box where the plug is now and run another 80 ft of wire for the new plug. Its a 30 amp, has 10/3 wire, from the junction on will 10/3 still be ok for the camper? Don't have the cash to buy all new wire. Don't wanna hurt the ac r anything else on the camper. Total run is probably 175 ft from the breaker.

    #2
    No. Total circuit length of 175, at 120V/30A requires #6AWG copper and that at 5% voltage drop which is allowed but not recommended.

    Even at 120V/20A it requires #8AWG copper.


    Sent from my iPad using Tapatalk Pro

    Comment


      #3
      If I use #6 from the junction box would it be OK, are would it need a whole new wire

      Comment


        #4
        I also have a 75ft rv extension cord I bought. Would I be able to use the cord instead of running the extra wire?

        Comment


          #5
          If you're gonna be on the place long enough, you need to wire as Mike d stated.

          Could always run triplex and take it with you

          I have a 45 foot run at the lake for a 50a and it's #6 x3 and an 8 ground.

          Sent from my SM-G970U using Tapatalk
          Last edited by Quackerbox; 03-29-2023, 08:08 PM.

          Comment


            #6
            Looked up 6/3, holly **** it's expensive.

            Comment


              #7
              .

              Comment


                #8
                Originally posted by Tyrex750 View Post
                Looked up 6/3, holly **** it's expensive.
                Look at the cost of the RV A/C and other electrical component replacement and it isn't so expensive. I ran 6/3 for a circuit a total of 120 feet and am still careful with what I run at the same time.

                Comment


                  #9
                  Move the trailer closer?

                  Comment


                    #10
                    I'm gonna look at it this weekend and see what's available

                    Comment


                      #11
                      PM sent

                      Comment


                        #12
                        Replied

                        Comment


                          #13
                          Your 75ft extension cord is probably 10AWG as well, so it's not any better than running 10AWG permanent wire.

                          You might could replace the 30 amp breaker with a 15 amp breaker. Voltage drop at 175ft would still be slightly over 5%, which isn't recommended but might be ok for a deer lease. Depending on your AC, you might trip the breaker. I can run the AC and a few LED lights in my camper on a 15A circuit at the house, but it will trip if anything else is running.

                          10AWG wire at 30A should be limited to less than 80ft; calculated from a simple voltage drop calculator... http://www.electrician2.com/calculat...r_initial.html

                          Comment


                            #14
                            So would 6/3 be the best route if I keep it at that distance? Going in the morning to look things over. Gonna look for a closer spot if possible.

                            Comment


                              #15
                              I have some #6 and 8 leftover at limestone. It's all stranded. And a few hundred feet of conduit.

                              I'd have to measure the wire to see length