Got on a lease and need to move the plug about 80 ft. I'm gonna pit a junction box where the plug is now and run another 80 ft of wire for the new plug. Its a 30 amp, has 10/3 wire, from the junction on will 10/3 still be ok for the camper? Don't have the cash to buy all new wire. Don't wanna hurt the ac r anything else on the camper. Total run is probably 175 ft from the breaker.
Announcement
Collapse
No announcement yet.
Rv electric plug question
Collapse
X
-
If you're gonna be on the place long enough, you need to wire as Mike d stated.
Could always run triplex and take it with you
I have a 45 foot run at the lake for a 50a and it's #6 x3 and an 8 ground.
Sent from my SM-G970U using TapatalkLast edited by Quackerbox; 03-29-2023, 08:08 PM.
Comment
-
Your 75ft extension cord is probably 10AWG as well, so it's not any better than running 10AWG permanent wire.
You might could replace the 30 amp breaker with a 15 amp breaker. Voltage drop at 175ft would still be slightly over 5%, which isn't recommended but might be ok for a deer lease. Depending on your AC, you might trip the breaker. I can run the AC and a few LED lights in my camper on a 15A circuit at the house, but it will trip if anything else is running.
10AWG wire at 30A should be limited to less than 80ft; calculated from a simple voltage drop calculator... http://www.electrician2.com/calculat...r_initial.html
Comment