    neutral or ground at 230 load?

    Comment


      #17
      Originally posted by Mike D View Post
      Why the reduced size neutral?


      Sent from my iPhone using Tapatalk Pro

      Because it’s permitted. When you order 4/0 Urd it comes with a 2/0 neutral. When you order #2 urd it comes with a #4 neutral.

      Check out 310.15(B)(7)(4) in 2017 code
      It moved to 310.12 (D) in 2020


      Sent from my iPhone using Tapatalk Pro

      Comment


        #18
        Originally posted by db@100 View Post
        You don't need the neutral for your 230 volt loads.

        I was assuming he was running to a sub panel in well house. That way he could have 120v lights and plugs in there. If he’s just feeding the well, you are correct. No neutral needed in that case.


        Sent from my iPhone using Tapatalk Pro

        Comment


          #19
          Originally posted by Huntindad View Post
          neutral or ground at 230 load?

          Make sure you run a neutral AND ground to all sub panel locations


          Sent from my iPhone using Tapatalk Pro

          Comment


            #20
            Yes, it will be to a sub panel in well house. Having lights and a an outlet comes in handy.

            Comment


              #21
              Originally posted by Huntindad View Post
              Yes, it will be to a sub panel in well house. Having lights and a an outlet comes in handy.

              Perfect. The wire and conduit sizes I stated are correct.


              Sent from my iPhone using Tapatalk Pro

              Comment


                #22
                Originally posted by FLASH_OUTDOORS View Post
                Make sure you run a neutral AND ground to all sub panel locations


                Sent from my iPhone using Tapatalk Pro
                that's the way I have it at my house now. My runs from main panel to subs are 50'

                Comment


                  #23
                  Question for the TBH electricians

                  Originally posted by Huntindad View Post
                  that's the way I have it at my house now. My runs from main panel to subs are 50'

                  You will put a 40a breaker at main service to well house. In the well house sub panel put a 30a for well and a 15-20a for lights and plugs.

                  In the main panel you will put a 100a breaker for shop.


                  Sent from my iPhone using Tapatalk Pro

                  Comment


                    #24
                    appreciate all the info.
                    What size sub panel is recomended for shop/well house?

                    Shop should/planned to have 1 50 amp breaker for welder and 3 20 amp breakers for lights/plugs.

                    Comment


                      #25
                      Originally posted by Huntindad View Post
                      appreciate all the info.
                      What size sub panel is recomended for shop/well house?

                      Shop should/planned to have 1 50 amp breaker for welder and 3 20 amp breakers for lights/plugs.

                      You can put a 6/12 panel in the well house. I would put a 12/24 in the shop. Both typically rated at 125a.


                      Sent from my iPhone using Tapatalk Pro

                      Comment


                        #26
                        one last question. I figure it is OK, but thought I would ask anyways.
                        My well house is on the way to shop. So...would it be OK to run both Conduits(well & shop) in same trench ? I would veer off to well for the well conduit. I figure to rent a 24" rocksaw to trench with.
                        A trencher may work with the rock layer, but I don't want to find out the hard way I was wrong.

                        Comment


                          #27
                          Originally posted by Huntindad View Post
                          one last question. I figure it is OK, but thought I would ask anyways.
                          My well house is on the way to shop. So...would it be OK to run both Conduits(well & shop) in same trench ? I would veer off to well for the well conduit. I figure to rent a 24" rocksaw to trench with.
                          A trencher may work with the rock layer, but I don't want to find out the hard way I was wrong.

                          Perfectly fine. Typical installs only require 18” of cover


                          Sent from my iPhone using Tapatalk Pro

                          Comment


                            #28
                            I know it’s allowed I’ve just never thought it to be good practice.


                            Sent from my iPhone using Tapatalk Pro

                            Comment


                              #29
                              Originally posted by FLASH_OUTDOORS View Post
                              I was assuming he was running to a sub panel in well house. That way he could have 120v lights and plugs in there. If he’s just feeding the well, you are correct. No neutral needed in that case.


                              Sent from my iPhone using Tapatalk Pro
                              Flash, my response was to the question "why the reduced size neutral". I was not saying he shouldn't pull a neutral to his subpanel.

                              Comment


                                #30
                                Do what Flash is saying.

                                Anything that feeds a sub panel has to have 4 wires.

                                you can down size the neut one size.

                                My house has a 200 amp feed through panel on a pole. about a 100 foot to the house. came off that panel with 100 amps to the shop