Hopefully someone that is smarter than I am is up at this hour. I'm wiring a mini split AC unit at the cabin. 220 from the cabin has a black, white and bare copper. The whip connecting the unit has black, red and green. How do I connect them?
sunsethunter is offline   Reply With Quote Back To The Top
Old 06-18-2021, 01:08 AM   #2
Terran28
Four Point
 
Join Date: Oct 2018
Location: White Settlement/FTW
Hunt In: Wherever is free and/or cheap
Default

you cannot!!! From the breaker box, you will need a double pole breaker in the amount required by the manufacturer of the unit, the proper gauge wire ran to the unit in to a disconnect box. The wires ran would be red and black with a ground. You CANNOT connect the red and black wires to the black and white wires of the cabin. If someone installed white and black wires to a 240 volt circuit, they are WRONG and will get someone seriously hurt or killed.
Terran28 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 01:29 AM   #3
sunsethunter
Ten Point
 
sunsethunter's Avatar
 
Join Date: Feb 2011
Location: Fort Worth
Hunt In: Sunset
Default

Quote:
Originally Posted by Terran28 View Post
you cannot!!! From the breaker box, you will need a double pole breaker in the amount required by the manufacturer of the unit, the proper gauge wire ran to the unit in to a disconnect box. The wires ran would be red and black with a ground. You CANNOT connect the red and black wires to the black and white wires of the cabin. If someone installed white and black wires to a 240 volt circuit, they are WRONG and will get someone seriously hurt or killed.

There is a double pole breaker in the box. I'm just confused by the wire colors and don't want to screw it up
sunsethunter is offline   Reply With Quote Back To The Top
Old 06-18-2021, 01:33 AM   #4
Terran28
Four Point
 
Join Date: Oct 2018
Location: White Settlement/FTW
Hunt In: Wherever is free and/or cheap
Default

call me with what you see. . Terran

Last edited by Terran28; 06-18-2021 at 02:25 AM.
Terran28 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 02:25 AM   #5
WTucker
Ten Point
 
WTucker's Avatar
 
Join Date: Aug 2016
Location: Orangefield
Default

For a 240 volt circuit that doesn’t need a neutral, it’s very common to run a romex with black, white, and bare. I am making the assumption this is what you have. If so, connect black to black, white to red, and bare to green. This is not going to kill anyone, again it’s very common/normal.
WTucker is offline   Reply With Quote Back To The Top
Old 06-18-2021, 02:47 AM   #6
sunsethunter
Ten Point
 
sunsethunter's Avatar
 
Join Date: Feb 2011
Location: Fort Worth
Hunt In: Sunset
Default

Quote:
Originally Posted by WTucker View Post
For a 240 volt circuit that doesnít need a neutral, itís very common to run a romex with black, white, and bare. I am making the assumption this is what you have. If so, connect black to black, white to red, and bare to green. This is not going to kill anyone, again itís very common/normal.

Got it. I got some step by step instructions and think I'll be good to go. Electricity surely isn't my thing
sunsethunter is offline   Reply With Quote Back To The Top
Old 06-18-2021, 05:16 AM   #7
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

Quote:
Originally Posted by Terran28 View Post
you cannot!!! From the breaker box, you will need a double pole breaker in the amount required by the manufacturer of the unit, the proper gauge wire ran to the unit in to a disconnect box. The wires ran would be red and black with a ground. You CANNOT connect the red and black wires to the black and white wires of the cabin. If someone installed white and black wires to a 240 volt circuit, they are WRONG and will get someone seriously hurt or killed.
Lol!
I assume you arenít an electrician?
Rubi513 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 05:27 AM   #8
Terran28
Four Point
 
Join Date: Oct 2018
Location: White Settlement/FTW
Hunt In: Wherever is free and/or cheap
Default

No, I am not. I have worked with my dad in HVAC for 30 years. Never have I EVER seen a 240 volt circuit use white/black/bare. I did research it and found no codes that state you cannot, however this is asinine and should have codes for it. If I see white/black, that is a 120 volt circuit. I will use my voltmeter to determine voltage, but If I see 240v running through black/white, I will walk away from it and tell them to get someone else or have an electrician rewire it with the proper 12/3 or 10/3 depending on load.
Terran28 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 05:32 AM   #9
PEC
Ten Point
 
PEC's Avatar
 
Join Date: Nov 2006
Location: Southeast Texas
Default

Quote:
Originally Posted by Terran28 View Post
you cannot!!! From the breaker box, you will need a double pole breaker in the amount required by the manufacturer of the unit, the proper gauge wire ran to the unit in to a disconnect box. The wires ran would be red and black with a ground. You CANNOT connect the red and black wires to the black and white wires of the cabin. If someone installed white and black wires to a 240 volt circuit, they are WRONG and will get someone seriously hurt or killed.
OK we are going to need some explanation...
1.What is the difference between red, black, ground or black, white, ground?
2. What if I don't use romex and pull in 3 single blacks? Will it explode?
3. What if we up grade and install (6/3 with a ground), what do we do with the 4th wire?
4. What if I connect red to black, black to white and green to bare?
PEC is offline   Reply With Quote Back To The Top
Old 06-18-2021, 05:41 AM   #10
Terran28
Four Point
 
Join Date: Oct 2018
Location: White Settlement/FTW
Hunt In: Wherever is free and/or cheap
Default

1. Red = load, black = load, white = neutral, green or bare is ground
2. 3 single black wires are all loads of a 3 phase circuit
3. You don't use the other wire, you wrap it around the rest (like I have seen every single time or cut it off)
4. If it is a splice , then you used the wrong first wire and should rerun with the properly colored wires. Other than that I do not understand your question.

Edit on 4. You can wire it like that and the circuit will work, however as I stated, if I see white, that is a neutral, always has been and have NEVER seen 14/2, 12/2, or 10/2 used ever in a 240v circuit

Last edited by Terran28; 06-18-2021 at 05:45 AM.
Terran28 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 05:56 AM   #11
Terran28
Four Point
 
Join Date: Oct 2018
Location: White Settlement/FTW
Hunt In: Wherever is free and/or cheap
Default

Guys, I understand my first comment to the OP was wrong in the eyes of electricians, but just stating I have never seen that (and until i just researched, thought it was wrong). I was taught differently by my dad. You be courteous to the "other guy" and use properly color coded wires to distinguish the circuit. If you HAVE to use different colored wires, you wrap tape around the ends of the wire to let them know it is a load bearing wire (black or red tape).

I have heard of technicians walking away from jobs because of this. They didn't want to become the liability because someone assumed that the white wire was a neutral.

Last edited by Terran28; 06-18-2021 at 05:58 AM.
Terran28 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 06:11 AM   #12
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

In residential work, you will see far more white conductors used for 240v than you will see red. Yes, it should be wrapped in tape to indicate it’s a hot.

If an electrician used “12/3 or 10/3” for a 240v load that didn’t require a neutral, he was throwing money away...
Rubi513 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 06:28 AM   #13
Terran28
Four Point
 
Join Date: Oct 2018
Location: White Settlement/FTW
Hunt In: Wherever is free and/or cheap
Default

Quote:
Originally Posted by Rubi513 View Post
In residential work, you will see far more white conductors used for 240v than you will see red. Yes, it should be wrapped in tape to indicate itís a hot.

If an electrician used ď12/3 or 10/3Ē for a 240v load that didnít require a neutral, he was throwing money away...
Every single residential 240v circuit I have seen has had the red wire it it. And the issue I see with that is if they reduced it back to 120 volt, then they have the black load line and the bare ground as neutral and the white line capped off...
Terran28 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 06:31 AM   #14
panhandlehunter
Pope & Young
 
panhandlehunter's Avatar
 
Join Date: Sep 2010
Location: Sweenyish
Hunt In: Brazoria, Matagorda & Webb Counties
Default

Quote:
Originally Posted by Terran28 View Post
Every single residential 240v circuit I have seen has had the red wire it it. And the issue I see with that is if they reduced it back to 120 volt, then they have the black load line and the bare ground as neutral and the white line capped off...
Well you learned something new. Never assume black/white=120V. Iím surprised you have never seen it, I would bet money it is that way on just about every house.
panhandlehunter is offline   Reply With Quote Back To The Top
Old 06-18-2021, 06:35 AM   #15
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

Quote:
Originally Posted by Terran28 View Post
Every single residential 240v circuit I have seen has had the red wire it it. And the issue I see with that is if they reduced it back to 120 volt, then they have the black load line and the bare ground as neutral and the white line capped off...
Then you havenít done much residential work.
So, youíre ok with someone using a bare ground as a neutral?
Rubi513 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 06:42 AM   #16
Terran28
Four Point
 
Join Date: Oct 2018
Location: White Settlement/FTW
Hunt In: Wherever is free and/or cheap
Default

Quote:
Originally Posted by Rubi513 View Post
Then you haven’t done much residential work.
So, you’re ok with someone using a bare ground as a neutral?
Actually I have seen it once and only once. In the house I live in as a matter of fact. The kitchen AC was 240 volt, when it was changed out before I moved in and converted to 120 volt, they used the black wire for hot, the bare ground for neutral and capped the white. I removed the cover plate to see what it would take to put in a duplex plug and discovered that. Haven't touched it since...

Last edited by Terran28; 06-18-2021 at 06:44 AM.
Terran28 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 06:52 AM   #17
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

A bare ground used as a neutral is more dangerous that a white wire not labeled as a hot.
Rubi513 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 07:26 AM   #18
Bowlife
Six Point
 
Bowlife's Avatar
 
Join Date: Jan 2016
Location: Danbury, TX
Default

Quote:
Originally Posted by Terran28 View Post
Guys, I understand my first comment to the OP was wrong in the eyes of electricians, but just stating I have never seen that (and until i just researched, thought it was wrong). I was taught differently by my dad. You be courteous to the "other guy" and use properly color coded wires to distinguish the circuit. If you HAVE to use different colored wires, you wrap tape around the ends of the wire to let them know it is a load bearing wire (black or red tape).

I have heard of technicians walking away from jobs because of this. They didn't want to become the liability because someone assumed that the white wire was a neutral.
The electricity flowing through the copper does not care what color the insulation is. It is absolutely normal for someone to run a 12/2 romex for a 240v circuit that does not require a neutral. It is also common to use the white as a switch leg or hot (depending on your personal preference) when wiring up lights and switches. It is common curtesy to label or mark the wires, but any electrician will tell you to never trust the color of a conductor. Thatís why you test it with a meter.
Bowlife is offline   Reply With Quote Back To The Top
Old 06-18-2021, 07:52 AM   #19
texasforever
Ten Point
 
Join Date: Oct 2014
Location: wharton
Hunt In: lavaca co.
Default

Bowlife has the right idea here. Yíallís answers of liability for using a black and white wire to run a 240v circuit are ridiculous. 94% of commercial work uses the whole rainbow for conductors, just gotta check it with a meter. If youíre worried about someone thinking itís a neutral because the wire is white just refer back to the Natural Selection page in the Book Of Life


Sent from my iPhone using Tapatalk
texasforever is offline   Reply With Quote Back To The Top
Old 06-18-2021, 08:26 AM   #20
kmitchl
Ten Point
 
Join Date: Aug 2011
Location: Montgomery, TX
Hunt In: Eldorado
Default

When i built my house i had this conversation with my electrician. We bet a lunch on it. In a circuit that consists of only 240 volt loads it is legal to run two phase conductors and ground. In a circuit with both 240 and 120 volt loads you must run a neutral conductor. I bought lunch.
kmitchl is offline   Reply With Quote Back To The Top
Old 06-18-2021, 08:33 AM   #21
panhandlehunter
Pope & Young
 
panhandlehunter's Avatar
 
Join Date: Sep 2010
Location: Sweenyish
Hunt In: Brazoria, Matagorda & Webb Counties
Default

Quote:
Originally Posted by texasforever View Post
Bowlife has the right idea here. Yíallís answers of liability for using a black and white wire to run a 240v circuit are ridiculous. 94% of commercial work uses the whole rainbow for conductors, just gotta check it with a meter. If youíre worried about someone thinking itís a neutral because the wire is white just refer back to the Natural Selection page in the Book Of Life


Sent from my iPhone using Tapatalk
Big difference between commercial, industrial and residential.
panhandlehunter is offline   Reply With Quote Back To The Top
Old 06-18-2021, 08:34 AM   #22
texasforever
Ten Point
 
Join Date: Oct 2014
Location: wharton
Hunt In: lavaca co.
Default

Quote:
Originally Posted by panhandlehunter View Post
Big difference between commercial, industrial and residential.

NEC applies the same in all applications


Sent from my iPhone using Tapatalk
texasforever is offline   Reply With Quote Back To The Top
Old 06-18-2021, 08:41 AM   #23
Arrow-Tek
Six Point
 
Join Date: Jan 2018
Default

Quote:
Originally Posted by Terran28 View Post
No, I am not. I have worked with my dad in HVAC for 30 years. Never have I EVER seen a 240 volt circuit use white/black/bare. I did research it and found no codes that state you cannot, however this is asinine and should have codes for it. If I see white/black, that is a 120 volt circuit. I will use my voltmeter to determine voltage, but If I see 240v running through black/white, I will walk away from it and tell them to get someone else or have an electrician rewire it with the proper 12/3 or 10/3 depending on load.
Surely youíve heard of phase tape? If your so scared of the white wire than put a little red tape on it.
Arrow-Tek is offline   Reply With Quote Back To The Top
Old 06-18-2021, 08:42 AM   #24
Mike D
Pope & Young
 
Mike D's Avatar
 
Join Date: Oct 2006
Location: North Texas
Hunt In: Haskell County, TX
Default

Quote:
Originally Posted by texasforever View Post
NEC applies the same in all applications


Sent from my iPhone using Tapatalk

Speaking of code, the code only specifically mentions 5 ďcolorsĒ and how they should be used:

Orange B phase of a 240 V Delta system indicating a ďhigh legĒ where it measures 240V to ground. White or grey to indicate a grounded conductor (neutral) and green or bare to indicate a grounding conductor.

It does allow provisions for marking the wires regardless of color such as with phase tape.

Even most modern residential wiring no longer uses the white as a switch leg which was a poor practice to begin with.


Sent from my iPhone using Tapatalk Pro
Mike D is offline   Reply With Quote Back To The Top
Old 06-18-2021, 08:50 AM   #25
texasforever
Ten Point
 
Join Date: Oct 2014
Location: wharton
Hunt In: lavaca co.
Default

Quote:
Originally Posted by Mike D View Post
Speaking of code, the code only specifically mentions 5 ďcolorsĒ and how they should be used:

Orange B phase of a 240 V Delta system indicating a ďhigh legĒ where it measures 240V to ground. White or grey to indicate a grounded conductor (neutral) and green or bare to indicate a grounding conductor.

It does allow provisions for marking the wires regardless of color such as with phase tape.

Even most modern residential wiring no longer uses the white as a switch leg which was a poor practice to begin with.


Sent from my iPhone using Tapatalk Pro

I agree, white as a switch leg is a horrible idea. On the other side of that running 10/3 or 8/3 for an A/C application is just a plain waste of money. Not a single unit out there that needs to utilize a neutral as all are straight 240 not 240/120. Only thing I could see that being useful is if the install tech wanted a 120v GFCI mounted inside the unit for servicing the unit. Most of the time what I run into is dual black conductors and a green, if three phase you might get lucky and have marking tape for the different phases providing itís not a delta system like mentioned. In the OPís application I personally donít see a need to distinguish between the different legs or have a neutral, systems gonna run the same if itís black on black or black on white.


Sent from my iPhone using Tapatalk
texasforever is offline   Reply With Quote Back To The Top
Old 06-18-2021, 08:53 AM   #26
panhandlehunter
Pope & Young
 
panhandlehunter's Avatar
 
Join Date: Sep 2010
Location: Sweenyish
Hunt In: Brazoria, Matagorda & Webb Counties
Default

Quote:
Originally Posted by texasforever View Post
NEC applies the same in all applications


Sent from my iPhone using Tapatalk
Yes, but still a big difference between a house and a chemical plant, which was my point.
panhandlehunter is offline   Reply With Quote Back To The Top
Old 06-18-2021, 09:34 AM   #27
silencer2011
Eight Point
 
silencer2011's Avatar
 
Join Date: Dec 2011
Location: Henrietta, TX
Hunt In: Clay County
Default

First of all, assuming that color of a wire is an indication of voltage is bad practice in all cases. Most people are correct that you don't typically see a 2 wire romex in a 240v, single phase application. On the other side of that, most residential 240v, 1 phase loads use some sort of small 120v load for a timer or a clock or something, and they need the neutral. This necessitates the 3/c - w/gnd. I have dealt with every color of the rainbow, and colors with tracer stripes. If it concerns you to phase tape the white and use it as a current carrying conductor, then pull a 3/c romex. In the end, its your place and you want to be happy and comfortable with it.
silencer2011 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 10:14 AM   #28
WTucker
Ten Point
 
WTucker's Avatar
 
Join Date: Aug 2016
Location: Orangefield
Default

Gotta love electrical threads where non-electricians jump in to give wrong advice. It’s always good to make sure you are talking with a licensed journeyman/master electrician when looking for advice.
WTucker is offline   Reply With Quote Back To The Top
Old 06-18-2021, 10:17 AM   #29
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

Quote:
Originally Posted by WTucker View Post
Gotta love electrical threads where non-electricians jump in to give wrong advice. Itís always good to make sure you are talking with a licensed journeyman/master electrician when looking for advice.
Rubi513 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 03:45 PM   #30
silencer2011
Eight Point
 
silencer2011's Avatar
 
Join Date: Dec 2011
Location: Henrietta, TX
Hunt In: Clay County
Default

Quote:
Originally Posted by WTucker View Post
Gotta love electrical threads where non-electricians jump in to give wrong advice. Itís always good to make sure you are talking with a licensed journeyman/master electrician when looking for advice.
Agreed. I got my daily entertainment out of it though.
silencer2011 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 09:13 PM   #31
Zmaxhunter
Four Point
 
Zmaxhunter's Avatar
 
Join Date: Feb 2021
Default

Sometimes i use brown, orange, and yellow. Lol
White wires are often used for hots, and if they are, they simply need a single band of black or red, or even blue phase tape..
Some of our residential houses have 240v 3phase services, they will have a 3ph meter, but only a single ph breaker panel.. the 3 phases will go from the meter to a 3ph disconnect, then straight to the a/c.

Would love to see some comments on a "california 3way" lol
Its how old timers wired 3way switches without travellers.
Basically, you use 2 3way switches, you wire the hot and neutral to each switch, then wire from each switch to the light., haha
The light works when it gets a hot from 1 switch and a neutral from the other.
Flipping a switch, the light goes out because it has 2 neutrals... or 2 HOTS, lmao

Last edited by Zmaxhunter; 06-18-2021 at 09:37 PM.
Zmaxhunter is offline   Reply With Quote Back To The Top
Old 06-18-2021, 09:31 PM   #32
Razorback01
Pope & Young
 
Razorback01's Avatar
 
Join Date: Nov 2006
Location: Johnson Co.
Hunt In: where my Elite takes me!
Default

A meter comes in handy most of the time, just sayin.
Razorback01 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 09:33 PM   #33
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: For a place
Default

Wow
Electrican is offline   Reply With Quote Back To The Top
Old 06-18-2021, 09:35 PM   #34
Mike D
Pope & Young
 
Mike D's Avatar
 
Join Date: Oct 2006
Location: North Texas
Hunt In: Haskell County, TX
Default

Quote:
Originally Posted by Zmaxhunter View Post
Sometimes i use brown, orange, and yellow. Lol

Would love to see some comments on a "california 3way" lol
Its how old timers wired 3way switches without travellers.
Basically, you use 2 3way switches, you wire the hot and neutral to each switch, then wire from each switch to the light., haha
The light works when it gets a hot from 1 switch and a neutral from the other.
Flipping a switch, the light goes out because it has 2 neutrals... or 2 HOTS, lmao

Iíve seen that once in 30+ years.


Sent from my iPhone using Tapatalk Pro
Mike D is offline   Reply With Quote Back To The Top
Old 06-18-2021, 09:42 PM   #35
Zmaxhunter
Four Point
 
Zmaxhunter's Avatar
 
Join Date: Feb 2021
Default

If you cant find the breaker to shut off the control power.. it might be because someone tapped the feeder, lol
Attached Images
 
Zmaxhunter is offline   Reply With Quote Back To The Top
Old 06-18-2021, 09:44 PM   #36
Zmaxhunter
Four Point
 
Zmaxhunter's Avatar
 
Join Date: Feb 2021
Default

I see california 3ways odten, in nearly all of these old early 1900s homes
Zmaxhunter is offline   Reply With Quote Back To The Top
Old 06-18-2021, 09:51 PM   #37
Zmaxhunter
Four Point
 
Zmaxhunter's Avatar
 
Join Date: Feb 2021
Default

This is the crap i deal with, old "A-base" style meters, these meters are "hard wired", you cannot unplug the meter.. you have to de-terminate the wires, while hot.. and usually the insulation breaks.. is brittle from being overheated.

Then, theres lots of indoor fuse boxes, mounted outside.!
Attached Images
 
Zmaxhunter is offline   Reply With Quote Back To The Top
Old 06-18-2021, 10:01 PM   #38
Zmaxhunter
Four Point
 
Zmaxhunter's Avatar
 
Join Date: Feb 2021
Default

Heres a good one i found recently. Its a 480v 3ph feed to a twist lock outlet on a column, for a welder.. no telling how many years it had been operating like this.. basically, the brown didnt get stripped when terminated.. but it still made enough connection when the voltage blew thru the thin flattened insulation.. smh
Attached Images
 
Zmaxhunter is offline   Reply With Quote Back To The Top
Old 06-18-2021, 10:16 PM   #39
Zmaxhunter
Four Point
 
Zmaxhunter's Avatar
 
Join Date: Feb 2021
Default

Heres another beauty..! Just kept adding wires to more fuse boxes or other loads. Another indoor fuse box mounted outside.. very large old home, 60amp service, they never upgrade them.. they just add on to what theyve got.. sad

Can see where it was burning up on the center.. neutral
Attached Images
 

Last edited by Zmaxhunter; 06-18-2021 at 10:19 PM.
Zmaxhunter is offline   Reply With Quote Back To The Top
Old 06-18-2021, 10:41 PM   #40
Quackerbox
Pope & Young
 
Quackerbox's Avatar
 
Join Date: Jul 2010
Location: Magnolia
Hunt In: The woods
Default

I wired my shop at the lake with black,red,blue and green,white

Commercial color in residence

Sent from my SM-G970U using Tapatalk
Quackerbox is offline   Reply With Quote Back To The Top
Old 06-18-2021, 11:01 PM   #41
Arrow-Tek
Six Point
 
Join Date: Jan 2018
Default

Quote:
Originally Posted by Quackerbox View Post
I wired my shop at the lake with black,red,blue and green,white

Commercial color in residence

Sent from my SM-G970U using Tapatalk
A 5 wire system? Please explain? Or pictures would be better to see whatís wired wrong.
Arrow-Tek is offline   Reply With Quote Back To The Top
Old 06-18-2021, 11:04 PM   #42
Zmaxhunter
Four Point
 
Zmaxhunter's Avatar
 
Join Date: Feb 2021
Default

3phases, neutral, ground... 5 wires
Zmaxhunter is offline   Reply With Quote Back To The Top
Old 06-18-2021, 11:05 PM   #43
Arrow-Tek
Six Point
 
Join Date: Jan 2018
Default

Quote:
Originally Posted by Zmaxhunter View Post
3phases, neutral, ground... 5 wires
He said to a residence? Never heard of a three phase residence?
Arrow-Tek is offline   Reply With Quote Back To The Top
Old 06-18-2021, 11:18 PM   #44
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

Quote:
Originally Posted by Arrow-Tek View Post
A 5 wire system? Please explain? Or pictures would be better to see whatís wired wrong.
He didnít say it was a 5 wire system...
He just said he used those colors.
It doesnít make anything ďwrongĒ.
Rubi513 is offline   Reply With Quote Back To The Top
Old 06-18-2021, 11:19 PM   #45
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

Quote:
Originally Posted by Arrow-Tek View Post
He said to a residence? Never heard of a three phase residence?

Not common, but I have.
It was 480v 3 phase...You can get what you want if you’re willing to pay.

Last edited by Rubi513; 06-18-2021 at 11:21 PM.
Rubi513 is offline   Reply With Quote Back To The Top
Old 06-19-2021, 12:00 AM   #46
Arrow-Tek
Six Point
 
Join Date: Jan 2018
Default

Quote:
Originally Posted by Rubi513 View Post
Not common, but I have.
It was 480v 3 phase...You can get what you want if youíre willing to pay.
Please excuse my ignorance Iíve only been a master electrician for 22 years and held a contractors license for 14 years and canít recall ever seeing three phase power available in a residential area. I have installed a lot of phase convertors in shops in residential areas.
Arrow-Tek is offline   Reply With Quote Back To The Top
Old 06-19-2021, 12:05 AM   #47
Briar Friar
Pope & Young
 
Briar Friar's Avatar
 
Join Date: May 2015
Default

Quote:
Originally Posted by Rubi513 View Post
In residential work, you will see far more white conductors used for 240v than you will see red. Yes, it should be wrapped in tape to indicate it’s a hot.

If an electrician used “12/3 or 10/3” for a 240v load that didn’t require a neutral, he was throwing money away...
I am lucky someone (installer/electrician) did this to an AC system at an inherited rental. I had a leg burn out or ground out err lightening strike err somechit. We ran on the other leg and disconnected grounded leg….as opposed to having to rerun entire line.

Thanks BigBaller…wherever you may be ballin.
Briar Friar is offline   Reply With Quote Back To The Top
Old 06-19-2021, 12:12 AM   #48
Zmaxhunter
Four Point
 
Zmaxhunter's Avatar
 
Join Date: Feb 2021
Default

Locally, in my little town of 2000, i can easily think of 6 homes with 3ph 240v.. its always a wild leg, 240v to ground.
We have our own generators, own power plant.. but we (the town) buy our power from a large provider, Evergy.. if we lose power from evergy, we can usually have our city generators online in about 15 min.. just cant afford to run them.. which is why they are backup only now.
When i was a kid, we always made our own power.. plant ran 247365
Zmaxhunter is offline   Reply With Quote Back To The Top
Old 06-19-2021, 12:22 AM   #49
Arrow-Tek
Six Point
 
Join Date: Jan 2018
Default

Quote:
Originally Posted by Zmaxhunter View Post
Locally, in my little town of 2000, i can easily think of 6 homes with 3ph 240v.. its always a wild leg, 240v to ground.
We have our own generators, own power plant.. but we (the town) buy our power from a large provider, Evergy.. if we lose power from evergy, we can usually have our city generators online in about 15 min.. just cant afford to run them.. which is why they are backup only now.
When i was a kid, we always made our own power.. plant ran 247365
Bet those three phase appliances were pretty expensive or the electrical service and transformer to convert to single phase power.
Arrow-Tek is offline   Reply With Quote Back To The Top
Old 06-19-2021, 12:28 AM   #50
Zmaxhunter
Four Point
 
Zmaxhunter's Avatar
 
Join Date: Feb 2021
Default

All it is used for is the AC compressor., the main house panel is normal single phase
Zmaxhunter is offline   Reply With Quote Back To The Top
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:25 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2021, vBulletin Solutions Inc.
Copyright 1999-2012, TexasBowhunter.com