Default AC Condensation Drain Advice

Well the inevitable happened this evening with a clogged AC condensation line. Came in and living room ceiling was soaked and dripping water. The drain ties in at the bathroom ptrap. Was able to get the clog free and water flowing again by taking it apart under sink and snaking it. The leak was coming from the pipe that appears to be a clean out pipe circled in pic. Is this a normal install as there is no cap or anything stopping the water? It was basically overflowing from the pipe. Could I put a removable cap to seal this so it overflows into pan if it happens again? Just canít believe there wouldnít be a cap on this. Thanks.
Attached Images
 
Electrican is offline   Reply With Quote Back To The Top
Old 09-15-2021, 10:33 PM   #2
txtimetravler
Pope & Young
 
txtimetravler's Avatar
 
Join Date: Oct 2006
Location: Tx
Hunt In: Wilco
Default

Pretty sure that open PVC is there to pour bleach inÖor force air to clean the line.

If that was capped, the clog would have still pushed water up until it leaked out.
txtimetravler is offline   Reply With Quote Back To The Top
Old 09-15-2021, 10:33 PM   #3
sideways
Ten Point
 
sideways's Avatar
 
Join Date: Nov 2009
Default

I have never seen it done this way cap that sucker.


Sent from my iPhone using Tapatalk
sideways is offline   Reply With Quote Back To The Top
Old 09-15-2021, 10:34 PM   #4
Oleman
Ten Point
 
Oleman's Avatar
 
Join Date: Oct 2006
Location: Burnet County
Hunt In: Anywhere I can
Default

I would cap it and run a separate line thru the outside wall. Best water for plants and outside trees or flowers. No more problem!
Oleman is offline   Reply With Quote Back To The Top
Old 09-15-2021, 10:35 PM   #5
sideways
Ten Point
 
sideways's Avatar
 
Join Date: Nov 2009
Default

The water should back up into an overflow pan not on your ceiling. One pan is built in one pan is under the unit. 2 drain lines 2 pans for fail safe.


Sent from my iPhone using Tapatalk
sideways is offline   Reply With Quote Back To The Top
Old 09-15-2021, 10:35 PM   #6
Smokeater
Ten Point
 
Join Date: Oct 2006
Location: Clifton,Tx
Hunt In: Tree
Default

Surprised it overflowed...unless that part of the line is lower that where it comes out of the unit. I'd sure put a cap on it.
Smokeater is online now   Reply With Quote Back To The Top
Old 09-15-2021, 10:38 PM   #7
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: For a place
Default

Quote:
Originally Posted by txtimetravler View Post
Pretty sure that open PVC is there to pour bleach inÖor force air to clean the line.

If that was capped, the clog would have still pushed water up until it leaked out.
Thatís what I think itís there for to. If it was capped it would have backed up into pan and drained outside on back porch. At least thatís what Iím thinking?? The pipe going to left goes outside on back porch in front of window.
Electrican is offline   Reply With Quote Back To The Top
Old 09-15-2021, 10:41 PM   #8
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: For a place
Default

Quote:
Originally Posted by Smokeater View Post
Surprised it overflowed...unless that part of the line is lower that where it comes out of the unit. I'd sure put a cap on it.
Now that you mention that, Iíll have to go check it. It sure doesnít look like itís much higher if any.
Electrican is offline   Reply With Quote Back To The Top
Old 09-15-2021, 10:46 PM   #9
rvd
Pope & Young
 
rvd's Avatar
 
Join Date: Dec 2008
Location: Gulf Coast
Hunt In: Texas
Default

I have a similar setup at bayhouse, mine is capped and the previous owner told me to pour bleach in it a couple times a year.
rvd is offline   Reply With Quote Back To The Top
Old 09-15-2021, 10:47 PM   #10
oktx
Pope & Young
 
oktx's Avatar
 
Join Date: Dec 2006
Location: Wise County
Hunt In: Wise County
Default

Your overflow is plugged also.
oktx is offline   Reply With Quote Back To The Top
Old 09-15-2021, 10:49 PM   #11
Smith
Four Point
 
Join Date: Aug 2012
Location: Dripping Springs
Hunt In: TX Hill Country and Panhandle
Default

Thatís called a breather stack. It keeps water flowing at a better pace than if it is capped, like like a vent on a sink or other plumbing fixtures. it also keeps the equipment from sucking water/air into the pipe above the p trap in some situations. It does need to be higher than the primary pan for the evaporator coil though. Basically higher than where the lines exit the coil box like someone else mentioned. Put a coupling and a few more inches of pipe on there.
Smith is offline   Reply With Quote Back To The Top
Old 09-15-2021, 10:50 PM   #12
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: For a place
Default

Quote:
Originally Posted by oktx View Post
Your overflow is plugged also.
The pipe coming out of unit and dumping straight into pan?
Electrican is offline   Reply With Quote Back To The Top
Old 09-15-2021, 10:54 PM   #13
Smith
Four Point
 
Join Date: Aug 2012
Location: Dripping Springs
Hunt In: TX Hill Country and Panhandle
Default

Overflow isn’t plugged. Water had somewhere to go (the short breather stack) and didn’t back up and go to the overflow.
Smith is offline   Reply With Quote Back To The Top
Old 09-15-2021, 10:57 PM   #14
Pstraw
Pope & Young
 
Join Date: Sep 2017
Location: Henderson
Hunt In: Front yard or back yard
Default

Mine has a cap on the pipe in question. However water can't overflow there as the overflow high level switch will shut the unit down before water gets that high.
Pstraw is online now   Reply With Quote Back To The Top
Old 09-15-2021, 11:07 PM   #15
oktx
Pope & Young
 
oktx's Avatar
 
Join Date: Dec 2006
Location: Wise County
Hunt In: Wise County
Default

Quote:
Originally Posted by Electrican View Post
The pipe coming out of unit and dumping straight into pan?
If your drain is plugged it should have gone into the overflow pan and drained outside instead of through your ceiling. My pipe is not capped. Iíve never seen one capped.
oktx is offline   Reply With Quote Back To The Top
Old 09-15-2021, 11:27 PM   #16
jdavidson
Associate Sponsor
 
jdavidson's Avatar
 
Join Date: Feb 2011
Location: Victoria
Hunt In: Webb Co
Default

Thereís two completely different types/scenarios of drain applications.
Positive side of evaporator requires one set up...negative side of evaporator requires totally different set up.
And if if you donít know the difference...stop
jdavidson is online now   Reply With Quote Back To The Top
Old 09-15-2021, 11:30 PM   #17
mpotts
Ten Point
 
mpotts's Avatar
 
Join Date: Jun 2010
Location: texas
Hunt In: Lometa Tx
Default

Mine was clogged up. I blew it out with a shop Vac.
mpotts is offline   Reply With Quote Back To The Top
Old 09-15-2021, 11:39 PM   #18
Starvin
Four Point
 
Starvin's Avatar
 
Join Date: Apr 2019
Location: Austin (was a good city)
Hunt In: Texas
Default

Quote:
Originally Posted by Smith View Post
Thatís called a breather stack. It keeps water flowing at a better pace than if it is capped, like like a vent on a sink or other plumbing fixtures. it also keeps the equipment from sucking water/air into the pipe above the p trap in some situations. It does need to be higher than the primary pan for the evaporator coil though. Basically higher than where the lines exit the coil box like someone else mentioned. Put a coupling and a few more inches of pipe on there.
Recommend this advice
Starvin is online now   Reply With Quote Back To The Top
Old 09-15-2021, 11:52 PM   #19
hpdrifter
Ten Point
 
Join Date: Sep 2014
Location: kerens
Hunt In: anywhere I can
Default

Quote:
Originally Posted by Electrican View Post
Thatís what I think itís there for to. If it was capped it would have backed up into pan and drained outside on back porch. At least thatís what Iím thinking?? The pipe going to left goes outside on back porch in front of window.
That's your clue. If that pipe by the window isn't dripping while the AC is in use, something is wrong.

It's put by a window for convenient viewing.

Peculiar; you get a owners manual for TV, computer, car, etc.
Do you get an owners manual for a house???
hpdrifter is offline   Reply With Quote Back To The Top
Old 09-15-2021, 11:53 PM   #20
Buck hunter332
Eight Point
 
Buck hunter332's Avatar
 
Join Date: Oct 2016
Hunt In: The water
Default

It’s a vent I believe
Buck hunter332 is offline   Reply With Quote Back To The Top
Old 09-15-2021, 11:55 PM   #21
Buck hunter332
Eight Point
 
Buck hunter332's Avatar
 
Join Date: Oct 2016
Hunt In: The water
Default

But I would Coupling it and put a 12 inch piece on it. it would have still leaked outta your p trap tho
Buck hunter332 is offline   Reply With Quote Back To The Top
Old 09-16-2021, 12:01 AM   #22
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: For a place
Default

Quote:
Originally Posted by hpdrifter View Post
That's your clue. If that pipe by the window isn't dripping while the AC is in use, something is wrong.

It's put by a window for convenient viewing.

Peculiar; you get a owners manual for TV, computer, car, etc.
Do you get an owners manual for a house???
How would it drip to the outside if there was no water in overflow pan? The external overflow pan under unit was completely dry.
Electrican is offline   Reply With Quote Back To The Top
Old 09-16-2021, 12:06 AM   #23
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: For a place
Default

I went up there and the vent stack is pretty much level with the top of drain pan fitting, if not slightly lower. Does it need to be higher? Would extending this up prevent this from happening again? And no cap needed?
Electrican is offline   Reply With Quote Back To The Top
Old 09-16-2021, 12:19 AM   #24
Starvin
Four Point
 
Starvin's Avatar
 
Join Date: Apr 2019
Location: Austin (was a good city)
Hunt In: Texas
Default

Quote:
Originally Posted by Electrican View Post
I went up there and the vent stack is pretty much level with the top of drain pan fitting, if not slightly lower. Does it need to be higher? Would extending this up prevent this from happening again? And no cap needed?
Yes. Raise the tee vent higher than the outlet on coil box. If this line stops up again the water will back up and drain out of the other coil box pipe that is directed to the pan on the floor (which will drain out the other line to outdoors)
Starvin is online now   Reply With Quote Back To The Top
Old 09-16-2021, 01:05 AM   #25
Artos
Pope & Young
 
Artos's Avatar
 
Join Date: Nov 2007
Location: Deep South TX
Hunt In: Deep South TX
Default

Shouldn't the pee trap be on the other side / down flow of the stack??
Artos is offline   Reply With Quote Back To The Top
Old 09-16-2021, 01:15 AM   #26
Dale Moser
Pope & Young
 
Dale Moser's Avatar
 
Join Date: Oct 2006
Location: Wise Cty
Hunt In: Young Cty
Default

The primary should drain into the main plumbing, the secondary should drain in front of a window, the pan should catch anything else in a last case scenario.

THey can all use some bleach from time to time, our primary clogs at least once a year if I don't put bleach in it.
Dale Moser is offline   Reply With Quote Back To The Top
Old 09-16-2021, 01:27 AM   #27
huntresss
Ten Point
 
huntresss's Avatar
 
Join Date: Oct 2006
Location: Stonewall, OK via Denton, TX
Hunt In: Pontotoc, OK
Default

We had the same thing happen. Our A/C guy installed a pan with a shut-off switch, so that if it ever overflowed again, it would shut the unit off before the pan overflowed onto our ceiling.
huntresss is offline   Reply With Quote Back To The Top
Old 09-16-2021, 04:57 AM   #28
hpdrifter
Ten Point
 
Join Date: Sep 2014
Location: kerens
Hunt In: anywhere I can
Default

Quote:
Originally Posted by Electrican View Post
How would it drip to the outside if there was no water in overflow pan? The external overflow pan under unit was completely dry.
I don't own a modern house that has built in AC like that.
I used to wire the houses that do, but it was a long time ago.
I might have that back wards: if the pipe by the window IS dripping, the main drain is clogged and needs attention.

One way or another, it is a visual clue that something is wrong with drain system.

That is a good question.

Last edited by hpdrifter; 09-16-2021 at 05:05 AM.
hpdrifter is offline   Reply With Quote Back To The Top
Old 09-16-2021, 05:52 AM   #29
tps7742
Ten Point
 
Join Date: Nov 2006
Location: Texas
Hunt In: East tx
Default

Quote:
Originally Posted by huntresss View Post
We had the same thing happen. Our A/C guy installed a pan with a shut-off switch, so that if it ever overflowed again, it would shut the unit off before the pan overflowed onto our ceiling.
From the homes I have owned they have been installing these cut off switches since the 90ís.
tps7742 is online now   Reply With Quote Back To The Top
Old 09-16-2021, 07:13 AM   #30
cva34
Ten Point
 
cva34's Avatar
 
Join Date: Sep 2016
Location: van vleck
Hunt In: LOOKING
Default

Quote:
Originally Posted by Smith View Post
Thatís called a breather stack. It keeps water flowing at a better pace than if it is capped, like like a vent on a sink or other plumbing fixtures. it also keeps the equipment from sucking water/air into the pipe above the p trap in some situations. It does need to be higher than the primary pan for the evaporator coil though. Basically higher than where the lines exit the coil box like someone else mentioned. Put a coupling and a few more inches of pipe on there.
Thats the way i understand it Too
cva34 is offline   Reply With Quote Back To The Top
Old 09-16-2021, 07:26 AM   #31
Duckologist
Ten Point
 
Join Date: Mar 2018
Location: SW Louisiana
Default

I had a new install done on my house about a year ago and the installer frowned upon bleach. He said the fumes from the bleach is bad for your unit and will eat it up much quicker. He says he only uses hot water about twice a year to keep the drain open. Said if you want to put something other than hot water you can mix some vinegar in with the water but bleach is too corrosive
Duckologist is offline   Reply With Quote Back To The Top
Old 09-16-2021, 07:58 AM   #32
DedDuk
Eight Point
 
Join Date: Aug 2018
Location: Onalaska
Hunt In: East and West TX
Default

Quote:
Originally Posted by Duckologist View Post
I had a new install done on my house about a year ago and the installer frowned upon bleach. He said the fumes from the bleach is bad for your unit and will eat it up much quicker. He says he only uses hot water about twice a year to keep the drain open. Said if you want to put something other than hot water you can mix some vinegar in with the water but bleach is too corrosive
Fumes wont get past the pee trap
DedDuk is online now   Reply With Quote Back To The Top
Old 09-16-2021, 08:11 AM   #33
Duckologist
Ten Point
 
Join Date: Mar 2018
Location: SW Louisiana
Default

Quote:
Originally Posted by DedDuk View Post
Fumes wont get past the pee trap
I don't argue with professionals lol.
Duckologist is offline   Reply With Quote Back To The Top
Old 09-16-2021, 10:46 AM   #34
savin yours
Pope & Young
 
savin yours's Avatar
 
Join Date: Feb 2007
Location: Texas
Hunt In: Lampasas
Default

Mine looked exactly like OPís. When I had a different company come out to work on it, I asked them if we could cap it because it was blowing cold air into my attic. He capped it and itís been like that for years. Should I take it off?


Sent from my iPhone using Tapatalk
savin yours is offline   Reply With Quote Back To The Top
Old 09-16-2021, 10:56 AM   #35
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: For a place
Default

So I ended up raising the vent riser 12” which is way above the drain entry. For extra assurance would capping it cause any problems with drainage? After seeing my ceiling damage now, I’m thinking I should eliminate any possibilities of water to come out of that open pipe. In other words force it to go into overflow pan and to outside drain if it ever clogs again.
Electrican is offline   Reply With Quote Back To The Top
Old 09-16-2021, 11:49 AM   #36
TeamAmerica
Ten Point
 
TeamAmerica's Avatar
 
Join Date: Oct 2016
Location: Dallas
Hunt In: Corsicana (Navarro County)
Default

You should install a switch! See pic. This will shut unit off via thermostat thus notifying you have a clog. You still want it at the right height for this to work.
TeamAmerica is online now   Reply With Quote Back To The Top
Old 09-16-2021, 12:26 PM   #37
Russ26
Spike
 
Join Date: Feb 2013
Default

A safety cut off switch on the pvc opening would kill the thermostat instead of keeping the unit running to continue overflowing. In addition to the periodic bleach, can hook up a shop vac on the outflow to suck out debris

Sent from my SM-G973U using Tapatalk
Russ26 is offline   Reply With Quote Back To The Top
Old 09-16-2021, 01:48 PM   #38
JFFB
Eight Point
 
Join Date: Dec 2019
Location: Ventress La.
Hunt In: Pointe Coupee
Default Switch

Quote:
Originally Posted by Electrican View Post
Well the inevitable happened this evening with a clogged AC condensation line. Came in and living room ceiling was soaked and dripping water. The drain ties in at the bathroom ptrap. Was able to get the clog free and water flowing again by taking it apart under sink and snaking it. The leak was coming from the pipe that appears to be a clean out pipe circled in pic. Is this a normal install as there is no cap or anything stopping the water? It was basically overflowing from the pipe. Could I put a removable cap to seal this so it overflows into pan if it happens again? Just canít believe there wouldnít be a cap on this. Thanks.
There is suppose to be a float switch in the pan.
JFFB is offline   Reply With Quote Back To The Top
Old 09-16-2021, 01:56 PM   #39
JFFB
Eight Point
 
Join Date: Dec 2019
Location: Ventress La.
Hunt In: Pointe Coupee
Thumbs up Correct

Quote:
Originally Posted by huntresss View Post
We had the same thing happen. Our A/C guy installed a pan with a shut-off switch, so that if it ever overflowed again, it would shut the unit off before the pan overflowed onto our ceiling.
We have winner. I have switch on mine to prevent this from happening.
JFFB is offline   Reply With Quote Back To The Top
Old 09-16-2021, 01:59 PM   #40
DedDuk
Eight Point
 
Join Date: Aug 2018
Location: Onalaska
Hunt In: East and West TX
Default

Quote:
Originally Posted by JFFB View Post
We have winner. I have switch on mine to prevent this from happening.
The issue in this case is the water wasnt going into the pan, it was coming out of the pipe. Float switch in the pan wouldnt fix this problem.
DedDuk is online now   Reply With Quote Back To The Top
Old 09-16-2021, 02:00 PM   #41
glen
Pope & Young
 
glen's Avatar
 
Join Date: Oct 2006
Location: Temporary transient
Hunt In: anywhere
Default

Your overflow is not working. Blow out or clean both lines. Make sure your trap has enough angle on it. But capping it does nothing. You need to be able to access that. I had caps on mine but never glued them
glen is offline   Reply With Quote Back To The Top
Old 09-16-2021, 02:04 PM   #42
bowhntrmatt
Pope & Young
 
bowhntrmatt's Avatar
 
Join Date: Dec 2009
Location: Wimberley
Hunt In: Comstock
Default

Tough to be sure by the pic, but it looks like you have a furnace setup so your drain is under positive air pressure. If so, that vent that leaked is positioned incorrectly. It should be upstream of the p trap and left open with a stack taller than the drain pan. This prevents the furnace from blowing the water out of the trap and making your sink gurgle in the winter. (Technically that setup doesn’t even need the trap but that’s a different conversation).

Definitely invest in a safety float switch to prevent this from happening again. And don’t listed to the guy that says you should have water dripping out over your window all the time. That’s wrong.
bowhntrmatt is online now   Reply With Quote Back To The Top
Old 09-16-2021, 02:32 PM   #43
Palmetto
Ten Point
 
Palmetto's Avatar
 
Join Date: Jan 2011
Location: Brazoria County
Default

Quote:
Originally Posted by bowhntrmatt View Post
Tough to be sure by the pic, but it looks like you have a furnace setup so your drain is under positive air pressure. If so, that vent that leaked is positioned incorrectly. It should be upstream of the p trap and left open with a stack taller than the drain pan. This prevents the furnace from blowing the water out of the trap and making your sink gurgle in the winter. (Technically that setup doesnít even need the trap but thatís a different conversation).

Definitely invest in a safety float switch to prevent this from happening again. And donít listed to the guy that says you should have water dripping out over your window all the time. Thatís wrong.
Quote:
Originally Posted by jdavidson View Post
Thereís two completely different types/scenarios of drain applications.
Positive side of evaporator requires one set up...negative side of evaporator requires totally different set up.
And if if you donít know the difference...stop
These guys are on the right track! Educate yourself on positive vs negative, and go from there.

I have a negative pressure system, and the clowns installed it like a positive pressure. It took me awhile to figure it out why it was overflowing the internal pan and leaking thru the sheet metal into the galvanized overflow. If you have a negative pressure system, then both the primary & secondary drains need to have a p-trap in order to drain correctly. If left open to atmosphere, it will create a vacuum and not let the condensate drain.

Also, I like to have my inspection port on the upstream side of the trap so that my bleach has to go thru the trap too.
Palmetto is offline   Reply With Quote Back To The Top
Old 09-16-2021, 04:06 PM   #44
JFFB
Eight Point
 
Join Date: Dec 2019
Location: Ventress La.
Hunt In: Pointe Coupee
Default

Quote:
Originally Posted by DedDuk View Post
The issue in this case is the water wasnt going into the pan, it was coming out of the pipe. Float switch in the pan wouldnt fix this problem.

Exactly I did not say it would. But it would stop the problem till the drain was fixed. Thanks


Sent from my iPhone using Tapatalk
JFFB is offline   Reply With Quote Back To The Top
Old 09-16-2021, 10:05 PM   #45
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: For a place
Default

Quote:
Originally Posted by bowhntrmatt View Post
Tough to be sure by the pic, but it looks like you have a furnace setup so your drain is under positive air pressure. If so, that vent that leaked is positioned incorrectly. It should be upstream of the p trap and left open with a stack taller than the drain pan. This prevents the furnace from blowing the water out of the trap and making your sink gurgle in the winter. (Technically that setup doesnít even need the trap but thatís a different conversation).

Definitely invest in a safety float switch to prevent this from happening again. And donít listed to the guy that says you should have water dripping out over your window all the time. Thatís wrong.
Yes it is a gas furnace setup. Weíve been here 9+ years and this is first problem ever. Never noticed any gurgling or other issues in winter time. It was simply clogged up at the ptrap under sink and backing up through the vent pipe that isnít capped. Iím going to look into these safety shutoffs as I donít want to deal with this again. Big area of sheet rock ruined in living room.
Electrican is offline   Reply With Quote Back To The Top
Old 09-16-2021, 10:12 PM   #46
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: For a place
Default

Quote:
Originally Posted by Palmetto View Post
These guys are on the right track! Educate yourself on positive vs negative, and go from there.

I have a negative pressure system, and the clowns installed it like a positive pressure. It took me awhile to figure it out why it was overflowing the internal pan and leaking thru the sheet metal into the galvanized overflow. If you have a negative pressure system, then both the primary & secondary drains need to have a p-trap in order to drain correctly. If left open to atmosphere, it will create a vacuum and not let the condensate drain.

Also, I like to have my inspection port on the upstream side of the trap so that my bleach has to go thru the trap too.
Thanks. I’m pretty well educated in the positive vs negative in the electricity world but not HVAC . I have had the unit serviced a couple different times and the “professionals” didn’t mention anything about it being wrong. It just puzzling that the water didn’t drain back into overflow pan and outside thru the viewing pipe
Electrican is offline   Reply With Quote Back To The Top
Old 09-16-2021, 10:40 PM   #47
JhuntsAlot
Eight Point
 
JhuntsAlot's Avatar
 
Join Date: Nov 2017
Location: Between Conroe and The Woodlands
Hunt In: Houston County, Madison County, Kendall County, where friends are.
Default

I used to install AC systems when I was younger. To be honest, was always told the p-trap and vent for the sink was was good enough. Any access near the coil was for clean out and was capped. But that was also 20+ years ago.

Did find this website with some interesting info on this.

https://cfacservice.com/home-ac-repairs/drain-lines/

Good info on the drain setup. Specifically where the vent should be.

I do think the p-trap you have is not ideal. You should probably get an actual sloping trap and not have the 90’s.



J
JhuntsAlot is offline   Reply With Quote Back To The Top
Old 09-16-2021, 10:43 PM   #48
Hunterdan
Moderator
 
Hunterdan's Avatar
 
Join Date: Aug 2008
Location: NE Houston
Hunt In: South Texas
Default

I just had a new A/C system installed and they told me to buy Main Line Cleaner from The Home Depot to pour down that drain pipe once a year to keep it clean.
Hunterdan is offline   Reply With Quote Back To The Top
Old 09-16-2021, 10:58 PM   #49
Starvin
Four Point
 
Starvin's Avatar
 
Join Date: Apr 2019
Location: Austin (was a good city)
Hunt In: Texas
Default

Quote:
Originally Posted by Electrican View Post
Thanks. Iím pretty well educated in the positive vs negative in the electricity world but not HVAC . I have had the unit serviced a couple different times and the ďprofessionalsĒ didnít mention anything about it being wrong. It just puzzling that the water didnít drain back into overflow pan and outside thru the viewing pipe
The problem has been addressed several times above for a simple fix. What you done should fix it, Suggest you test it. Then call a tech out to install a safety float switch and the tech can explain what happened when the tee outlet is lower than the main drain outlet (when the water backs up it will come out of the lowest opening) Good Luck
Starvin is online now   Reply With Quote Back To The Top
Old 09-17-2021, 12:18 AM   #50
jdavidson
Associate Sponsor
 
jdavidson's Avatar
 
Join Date: Feb 2011
Location: Victoria
Hunt In: Webb Co
Default

If itís a gas system and the coil is IN FRONT of the blower ( trust me it is )... then get rid of the P trap.

P trap are necessary ONLY on negative pressure systems (electric)
jdavidson is online now   Reply With Quote Back To The Top
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 08:32 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2022, vBulletin Solutions Inc.
Copyright 1999-2012, TexasBowhunter.com