Default Electrical and water line in Trench question

I need to run power and water to my shop that is 175ft away and will cross a gravel driveway. I want to run the electric conduit and the water in the same trench. How deep should I go. I was thinking 36 inch for the conduit fill in about 12 inches and put the water line on top of that. Is this over kill or about right? One section will eventually get a slab poured over it for a garage.

Last edited by sharkhunter; 05-14-2019 at 10:05 PM.
sharkhunter is offline   Reply With Quote Back To The Top
Old 05-14-2019, 09:56 PM   #2
FLASH_OUTDOORS
Ten Point
 
FLASH_OUTDOORS's Avatar
 
Join Date: Aug 2012
Location: Tomball
Hunt In: Kennard
Default

You can run them in same trench. 24” for electrical conduit under concrete carrying weight. You can put water right next to it. Doesn’t matter.


Sent from my iPhone using Tapatalk
FLASH_OUTDOORS is offline   Reply With Quote Back To The Top
Old 05-14-2019, 09:58 PM   #3
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

18” will work for the electrical.
Rubi513 is offline   Reply With Quote Back To The Top
Old 05-14-2019, 09:58 PM   #4
FLASH_OUTDOORS
Ten Point
 
FLASH_OUTDOORS's Avatar
 
Join Date: Aug 2012
Location: Tomball
Hunt In: Kennard
Default

Quote:
Originally Posted by Rubi513 View Post
18” will work for the electrical.


Not under a drive way.


Sent from my iPhone using Tapatalk
FLASH_OUTDOORS is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:01 PM   #5
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

Quote:
Originally Posted by FLASH_OUTDOORS View Post
Not under a drive way.


Sent from my iPhone using Tapatalk
Under a dwelling driveway.
Rubi513 is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:02 PM   #6
sharkhunter
Pope & Young
 
sharkhunter's Avatar
 
Join Date: Dec 2006
Location: Tarkington , TX
Hunt In: In the woods
Default

Quote:
Originally Posted by FLASH_OUTDOORS View Post
Not under a drive way.


Sent from my iPhone using Tapatalk
I was a little worried about that because some dump trucks and delivery trucks will be driving over it at times. Not a lot but it will happen.
sharkhunter is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:04 PM   #7
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

Quote:
Originally Posted by sharkhunter View Post
I was a little worried about that because some dump trucks and delivery trucks will be driving over it at times. Not a lot but it will happen.
You can bury it as deep as you want. As far as Code goes, 18” is minimum for a residential driveway.
Rubi513 is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:07 PM   #8
bmac
Ten Point
 
bmac's Avatar
 
Join Date: Jun 2009
Location: Weatherford
Hunt In: Robertson Co. & TPWD
Default Electrical and water line in Trench question

Is conduit a must or is UF cable an option if worried about crushing conduit? I like raceways as you can replace if needed but not required. If ground is soft then deeper is better and not that much more time with a good trencher.


Sent from my iPhone using Tapatalk
bmac is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:08 PM   #9
FLASH_OUTDOORS
Ten Point
 
FLASH_OUTDOORS's Avatar
 
Join Date: Aug 2012
Location: Tomball
Hunt In: Kennard
Default

Quote:
Originally Posted by Rubi513 View Post
You can bury it as deep as you want. As far as Code goes, 18” is minimum for a residential driveway.


Rubi is right. The minimum is 18” in residential drives. I always go the route better safe than sorry under drives. Driveways is 24”. “Dwelling driveways” are 18”. If I’m digging a ditch, what’s an extra 6”??


Sent from my iPhone using Tapatalk
FLASH_OUTDOORS is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:09 PM   #10
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

Quote:
Originally Posted by FLASH_OUTDOORS View Post
what’s an extra 6”??


Sent from my iPhone using Tapatalk
Doing electrical work, or making movies...
Rubi513 is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:12 PM   #11
Hoss163
Ten Point
 
Hoss163's Avatar
 
Join Date: Jul 2016
Location: Abilene tx
Hunt In: Oklahoma
Default

Lay it a few inches apart at least. Don’t have it touching at all what ever you do


Sent from my iPhone using Tapatalk
Hoss163 is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:13 PM   #12
FLASH_OUTDOORS
Ten Point
 
FLASH_OUTDOORS's Avatar
 
Join Date: Aug 2012
Location: Tomball
Hunt In: Kennard
Default

Quote:
Originally Posted by Hoss163 View Post
Lay it a few inches apart at least. Don’t have it touching at all what ever you do


Sent from my iPhone using Tapatalk


Why? They will both be in conduit.


Sent from my iPhone using Tapatalk
FLASH_OUTDOORS is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:15 PM   #13
Hoss163
Ten Point
 
Hoss163's Avatar
 
Join Date: Jul 2016
Location: Abilene tx
Hunt In: Oklahoma
Default

If you ever have to work on the water line that’s why don’t want to wrestle another pipe right next to it if you have to ever repair it .


Sent from my iPhone using Tapatalk
Hoss163 is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:17 PM   #14
Hoss163
Ten Point
 
Hoss163's Avatar
 
Join Date: Jul 2016
Location: Abilene tx
Hunt In: Oklahoma
Default

Quote:
Originally Posted by FLASH_OUTDOORS View Post
Why? They will both be in conduit.


Sent from my iPhone using Tapatalk
I hope your not running the water line out of conduit.
Hoss163 is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:19 PM   #15
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

Quote:
Originally Posted by Hoss163 View Post
I hope your not running the water line out of conduit.
What else would you put it in?
Rubi513 is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:21 PM   #16
FLASH_OUTDOORS
Ten Point
 
FLASH_OUTDOORS's Avatar
 
Join Date: Aug 2012
Location: Tomball
Hunt In: Kennard
Default

Let me clarify for the OP. For safety and legal purposes, there is no reason what so ever, you can’t put them both in same ditch. The MINIMUM COVER the code requires under a residential drive is 18”. Any drive other than residential is 24”. If I was digging the ditch and expected heavy traffic I would go the extra 6”.


Sent from my iPhone using Tapatalk
FLASH_OUTDOORS is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:22 PM   #17
Hoss163
Ten Point
 
Hoss163's Avatar
 
Join Date: Jul 2016
Location: Abilene tx
Hunt In: Oklahoma
Default

Quote:
Originally Posted by Rubi513 View Post
What else would you put it in?


White pvc pipe for water



Sent from my iPhone using Tapatalk
Hoss163 is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:22 PM   #18
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

Quote:
Originally Posted by Hoss163 View Post
White pvc pipe for water



Sent from my iPhone using Tapatalk
That’s considered conduit...PVC conduit.
Rubi513 is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:23 PM   #19
bmac
Ten Point
 
bmac's Avatar
 
Join Date: Jun 2009
Location: Weatherford
Hunt In: Robertson Co. & TPWD
Default

Quote:
Originally Posted by Rubi513 View Post
What else would you put it in?


I like to just use cheap garden hoses


Sent from my iPhone using Tapatalk
bmac is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:25 PM   #20
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

Quote:
Originally Posted by bmac View Post
I like to just use cheap garden hoses


Sent from my iPhone using Tapatalk
Rubi513 is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:26 PM   #21
Hoss163
Ten Point
 
Hoss163's Avatar
 
Join Date: Jul 2016
Location: Abilene tx
Hunt In: Oklahoma
Default

Conduit is grey pipe . Are silver metal pipe not white Pvc


Sent from my iPhone using Tapatalk
Hoss163 is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:28 PM   #22
FLASH_OUTDOORS
Ten Point
 
FLASH_OUTDOORS's Avatar
 
Join Date: Aug 2012
Location: Tomball
Hunt In: Kennard
Default

Quote:
Originally Posted by Hoss163 View Post
Conduit is grey pipe . Are silver metal pipe not white Pvc


Sent from my iPhone using Tapatalk






Sent from my iPhone using Tapatalk
FLASH_OUTDOORS is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:31 PM   #23
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

https://www.thefreedictionary.com/plumbing+conduit

Edit. Flash beat me.
Rubi513 is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:33 PM   #24
sharkhunter
Pope & Young
 
sharkhunter's Avatar
 
Join Date: Dec 2006
Location: Tarkington , TX
Hunt In: In the woods
Default

Just for clarification for the electrical I’m going to run 4/0 wire in 2” sch40 gray pvc conduit. For the water planing to run 1-1/4 sch40 white pvc
sharkhunter is offline   Reply With Quote Back To The Top
Old 05-14-2019, 10:36 PM   #25
FLASH_OUTDOORS
Ten Point
 
FLASH_OUTDOORS's Avatar
 
Join Date: Aug 2012
Location: Tomball
Hunt In: Kennard
Default

Quote:
Originally Posted by sharkhunter View Post
Just for clarification for the electrical I’m going to run 4/0 wire in 2” sch40 gray pvc conduit. For the water planing to run 1-1/4 sch40 white pvc


You are correct in your sizing on the electrical conduit. Will this be sub-fed from an existing service? If so run a #4 ground wire also. Separate your grounds and neutrals on the new side.


Sent from my iPhone using Tapatalk
FLASH_OUTDOORS is offline   Reply With Quote Back To The Top
Old 05-14-2019, 11:04 PM   #26
sharkhunter
Pope & Young
 
sharkhunter's Avatar
 
Join Date: Dec 2006
Location: Tarkington , TX
Hunt In: In the woods
Default

Quote:
Originally Posted by FLASH_OUTDOORS View Post
You are correct in your sizing on the electrical conduit. Will this be sub-fed from an existing service? If so run a #4 ground wire also. Separate your grounds and neutrals on the new side.


Sent from my iPhone using Tapatalk
I’m not up on electrical terminology so not sure what a sub feed is. I have an electrician I’m going to bring on to help me on the hookups to make sure all is right. What I have now is right after the meter the service goes to a header box. Going into the box is my generator and coming out is my breaker box. I don’t want the generator running the shop so he’s going to tie into the header and go to a disconnect then out to my shop so I will not be going though the breaker box of the house. Do you think I need to separate the ground if ran like this? What would be the advantages of that? Thanks everyone for your help.
sharkhunter is offline   Reply With Quote Back To The Top
Old 05-15-2019, 12:43 AM   #27
Duane
Ten Point
 
Duane's Avatar
 
Join Date: Oct 2006
Location: Missouri City TX
Hunt In: Brady TX
Default

Quote:
Originally Posted by sharkhunter View Post
I’m not up on electrical terminology so not sure what a sub feed is. I have an electrician I’m going to bring on to help me on the hookups to make sure all is right. What I have now is right after the meter the service goes to a header box. Going into the box is my generator and coming out is my breaker box. I don’t want the generator running the shop so he’s going to tie into the header and go to a disconnect then out to my shop so I will not be going though the breaker box of the house. Do you think I need to separate the ground if ran like this? What would be the advantages of that? Thanks everyone for your help.
Flash will correct me if I'm wrong but what you describe would not be a subpanel, so you can ground your neutral at the new shop panel. Drive a rod near the shop panel and ground your panel there, then tie your neutral and ground bars inside the panel.

If you were feeding your shop panel from a breaker in your existing panel, you would not ground the neutral in the shop subpanel. Neutral would only be grounded at the main.
Duane is offline   Reply With Quote Back To The Top
Old 05-15-2019, 05:36 AM   #28
Tony Pic
Pope & Young
 
Tony Pic's Avatar
 
Join Date: Feb 2013
Location: NYS and Texas
Hunt In: The Picarosas North and South, Kerrville, Mountain Home and Harper
Default

Quote:
Originally Posted by Hoss163 View Post
Conduit is grey pipe . Are silver metal pipe not white Pvc


Sent from my iPhone using Tapatalk
For the record...I was in construction for 35 years. Conduit is always referred to as a electrical pipe.
Water raceways have always been referred to as just water pipe. Copper or plastic(pex).
Schedule 40 is standard wall thickness. Schedule 80 is heavy wall PVC conduit for that extra strength pipe wall. I believe the white water PVC is measured in the same way, sched 40 & 80 for wall thickness.
I have only heard people not in the trades refer to a water pipe as a water conduit.

You have truck traffic? Hard coliche? Use the schedule 80 PVC.
Tony Pic is offline   Reply With Quote Back To The Top
Old 05-15-2019, 06:13 AM   #29
FLASH_OUTDOORS
Ten Point
 
FLASH_OUTDOORS's Avatar
 
Join Date: Aug 2012
Location: Tomball
Hunt In: Kennard
Default

Quote:
Originally Posted by sharkhunter View Post
I’m not up on electrical terminology so not sure what a sub feed is. I have an electrician I’m going to bring on to help me on the hookups to make sure all is right. What I have now is right after the meter the service goes to a header box. Going into the box is my generator and coming out is my breaker box. I don’t want the generator running the shop so he’s going to tie into the header and go to a disconnect then out to my shop so I will not be going though the breaker box of the house. Do you think I need to separate the ground if ran like this? What would be the advantages of that? Thanks everyone for your help.


Ok sorry, I passed out last night. Everything after the first point of disconnect is a sub feed. Your first point of disconnect for the shop will be at the main service at your house. This needs to be the ONLY place that your neutrals and grounds are together. Every location after that will need to be separated. You will need a main breaker at the shop also because it is a separate structure. Also a ground rod. In this situation you will need the separate ground wire.


Sent from my iPhone using Tapatalk
FLASH_OUTDOORS is offline   Reply With Quote Back To The Top
Old 05-15-2019, 06:32 AM   #30
Traildust
Pope & Young
 
Traildust's Avatar
 
Join Date: Apr 2007
Location: Alvin, Texas
Hunt In: Bee County
Default

Quote:
Originally Posted by Tony Pic View Post
For the record...I was in construction for 35 years. Conduit is always referred to as a electrical pipe.
Water raceways have always been referred to as just water pipe. Copper or plastic(pex).
Schedule 40 is standard wall thickness. Schedule 80 is heavy wall PVC conduit for that extra strength pipe wall. I believe the white water PVC is measured in the same way, sched 40 & 80 for wall thickness.
I have only heard people not in the trades refer to a water pipe as a water conduit.

You have truck traffic? Hard coliche? Use the schedule 80 PVC.
Lol....conduit is for wires! Water conduit is something I expect to hear at Home Depot!



That's almost as stupid as a hose pipe!

I buried my water and elect 36" deep in the same hole. That trencher dont care!

Last edited by Traildust; 05-15-2019 at 06:35 AM.
Traildust is offline   Reply With Quote Back To The Top
Old 05-15-2019, 07:24 AM   #31
OldRiverRat
Ten Point
 
OldRiverRat's Avatar
 
Join Date: Mar 2009
Location: Deer Park, TX
Hunt In: Navarro County
Default

I wouldn’t even use conduit, I’d use UF and save the money and hassle. Lay the wire in the same trench and get it done


Sent from my iPhone using Tapatalk Pro
OldRiverRat is offline   Reply With Quote Back To The Top
Old 05-15-2019, 08:11 AM   #32
meltingfeather
Ten Point
 
Join Date: Oct 2012
Location: austin
Hunt In: Gillespie, San Saba & Kerr primarily
Default

Quote:
Originally Posted by Tony Pic View Post
For the record...I was in construction for 35 years. Conduit is always referred to as a electrical pipe.
But it say so the de dictionary!
meltingfeather is offline   Reply With Quote Back To The Top
Old 05-15-2019, 08:41 AM   #33
E.TX.BOWHUNTER
Ten Point
 
E.TX.BOWHUNTER's Avatar
 
Join Date: Nov 2009
Location: East Texas
Hunt In: Texas Public Lands
Default

I had just done this. My requirement from elec co. was a 2-1/2" conduit 30" deep. I ran water in the same trench 12" above electrical conduit.
E.TX.BOWHUNTER is offline   Reply With Quote Back To The Top
Old 05-15-2019, 08:46 AM   #34
bwssr
Pope & Young
 
bwssr's Avatar
 
Join Date: Oct 2006
Location: Madisonville, Texas
Hunt In: Madison county
Default

When you start to cover these...put 6 or so inches of dirt in, the lay yellow caution or red danger tape/robin in the trench. So if you later on, or someone else digs the tape I will be seen first
bwssr is offline   Reply With Quote Back To The Top
Old 05-15-2019, 08:58 AM   #35
RWB
Eight Point
 
RWB's Avatar
 
Join Date: May 2011
Location: Magnolia
Hunt In: Leon County
Default

Quote:
Originally Posted by bwssr View Post
When you start to cover these...put 6 or so inches of dirt in, the lay yellow caution or red danger tape/robin in the trench. So if you later on, or someone else digs the tape I will be seen first
That's a good idea....I built my house and shop and even I cant exactly remember how everything ran after a few years
RWB is offline   Reply With Quote Back To The Top
Old 05-15-2019, 09:49 AM   #36
Tony Pic
Pope & Young
 
Tony Pic's Avatar
 
Join Date: Feb 2013
Location: NYS and Texas
Hunt In: The Picarosas North and South, Kerrville, Mountain Home and Harper
Default

Quote:
Originally Posted by meltingfeather View Post
But it say so the de dictionary!
Yes sir brother I totally agree, that is what the book says.
But you sound like a green horn saying it. That is all I'm saying.
Tony Pic is offline   Reply With Quote Back To The Top
Old 05-15-2019, 10:14 AM   #37
dhillis
Ten Point
 
dhillis's Avatar
 
Join Date: Nov 2008
Location: Aransas Pass
Hunt In: Aransas Pass, San Marcos
Default

I ran electrical from the pole to my house, and water from the well to the house. Well and electrical pole were close to each other, so they ran in the same trench 90% of the way to the house. The electrical from pole to house was 200 amps, so we buried it about 5' deep in a 4" pvc. Filled back about 18" then ran water, then filled in trench
dhillis is offline   Reply With Quote Back To The Top
Old 05-15-2019, 10:25 AM   #38
Kossetx
Six Point
 
Join Date: Jan 2017
Default

this is Websters definition.

Definition of conduit
1 : a natural or artificial channel through which something (such as a fluid) is conveyed
a conduit for rainwater
2 : a pipe, tube, or tile for protecting electric wires or cables
3 : a means of transmitting or distributing

There is a difference between channel and pipe/tube.
Kossetx is offline   Reply With Quote Back To The Top
Old 05-15-2019, 10:51 AM   #39
gusman
Ten Point
 
gusman's Avatar
 
Join Date: Mar 2010
Location: magnolia,tx
Hunt In: Drag racing
Default

Quote:
Originally Posted by Hoss163 View Post
I hope your not running the water line out of conduit.
LoL why run 2 lines just run wire in the water line..
gusman is offline   Reply With Quote Back To The Top
Old 05-15-2019, 11:16 AM   #40
meltingfeather
Ten Point
 
Join Date: Oct 2012
Location: austin
Hunt In: Gillespie, San Saba & Kerr primarily
Default

Quote:
Originally Posted by Tony Pic View Post
Yes sir brother I totally agree, that is what the book says.

But you sound like a green horn saying it. That is all I'm saying.
For sure... I was kidding.

My BIL wanted to sound like he knew what he was talking about when he went to the electrical supply house and asked for “four aug” wire for his RV service. What he needed was No. 4 AWG (he pronounced the AWG) and what he got was 0000. We had a heck of a time wresting that stuff into a 30A receptacle box!!
meltingfeather is offline   Reply With Quote Back To The Top
Old 05-15-2019, 11:17 AM   #41
meltingfeather
Ten Point
 
Join Date: Oct 2012
Location: austin
Hunt In: Gillespie, San Saba & Kerr primarily
Default

Quote:
Originally Posted by Kossetx View Post
this is Websters definition.

Definition of conduit
1 : a natural or artificial channel through which something (such as a fluid) is conveyed
a conduit for rainwater
2 : a pipe, tube, or tile for protecting electric wires or cables
3 : a means of transmitting or distributing

There is a difference between channel and pipe/tube.
Ask a plumber to come put in conduit for you and he’ll tell you to call an electrician.
meltingfeather is offline   Reply With Quote Back To The Top
Old 05-15-2019, 05:31 PM   #42
outlook8
Ten Point
 
outlook8's Avatar
 
Join Date: Apr 2008
Location: Houston
Hunt In: TX
Default

Quote:
Originally Posted by gusman View Post
LoL why run 2 lines just run wire in the water line..
Yep, just size up the electrical pipe for the water pressure. No need for a water conduit!
outlook8 is offline   Reply With Quote Back To The Top
Old 05-15-2019, 05:53 PM   #43
DallasCoon12
Four Point
 
DallasCoon12's Avatar
 
Join Date: Oct 2018
Location: Kerrville
Hunt In: Kerr County, México
Default

Even though it’s just a gravel driveway it’s pretty cheap to sleeve them with a larger size pvc pipe. This will protect the pipe/conduit as well as simplify replacement. Definitely sleeve it if it was concrete.
DallasCoon12 is offline   Reply With Quote Back To The Top
Old 05-15-2019, 06:51 PM   #44
MBV77
Ten Point
 
MBV77's Avatar
 
Join Date: Feb 2013
Location: Whitesboro, TX.
Hunt In: Clay County
Default

Quote:
Originally Posted by Traildust View Post
Lol....conduit is for wires! Water conduit is something I expect to hear at Home Depot!



That's almost as stupid as a hose pipe!

I buried my water and elect 36" deep in the same hole. That trencher dont care!


What’s hose pipe?.....Poly?


Sent from my iPhone using Tapatalk
MBV77 is online now   Reply With Quote Back To The Top
Old 05-15-2019, 09:15 PM   #45
Tony Pic
Pope & Young
 
Tony Pic's Avatar
 
Join Date: Feb 2013
Location: NYS and Texas
Hunt In: The Picarosas North and South, Kerrville, Mountain Home and Harper
Default

Quote:
Originally Posted by meltingfeather View Post
For sure... I was kidding.

My BIL wanted to sound like he knew what he was talking about when he went to the electrical supply house and asked for “four aug” wire for his RV service. What he needed was No. 4 AWG (he pronounced the AWG) and what he got was 0000. We had a heck of a time wresting that stuff into a 30A receptacle box!!
That is funny 😁. Big price difference.
The 0000 designation is actually pronounced like aught...yup like thirty aught six.
You would be asking for 4 aught wire. AWG stands for american wire gauge😉.
Tony Pic is offline   Reply With Quote Back To The Top
Old 05-15-2019, 10:11 PM   #46
merlin
Eight Point
 
Join Date: Jun 2015
Default

I advise against putting them in same ditch. Water and electric don't mix.
merlin is offline   Reply With Quote Back To The Top
Old 05-15-2019, 10:28 PM   #47
sharkhunter
Pope & Young
 
sharkhunter's Avatar
 
Join Date: Dec 2006
Location: Tarkington , TX
Hunt In: In the woods
Default

Quote:
Originally Posted by bwssr View Post
When you start to cover these...put 6 or so inches of dirt in, the lay yellow caution or red danger tape/robin in the trench. So if you later on, or someone else digs the tape I will be seen first
Good idea. My dad also said to put galvanized wire in the ditch about 6 inch from the top so you can find it with a metal detector.
sharkhunter is offline   Reply With Quote Back To The Top
Old 05-15-2019, 10:37 PM   #48
WTucker
Eight Point
 
WTucker's Avatar
 
Join Date: Aug 2016
Location: Orangefield
Hunt In: Votaw
Default

Quote:
Originally Posted by merlin View Post
I advise against putting them in same ditch. Water and electric don't mix.
Being in the same ditch won’t matter. The conduit will probably end up with water in it anyway.
WTucker is online now   Reply With Quote Back To The Top
Old 05-15-2019, 10:40 PM   #49
Mike D
Pope & Young
 
Mike D's Avatar
 
Join Date: Oct 2006
Location: North Texas
Hunt In: Haskell County, TX
Default

Quote:
Originally Posted by merlin View Post
I advise against putting them in same ditch. Water and electric don't mix.


You’d really freak out to know that shared ditches are common. I’ve run water, electric, telephone and gas all in a combined ditch on several large commercial projects.


Sent from my iPhone using Tapatalk Pro
Mike D is offline   Reply With Quote Back To The Top
Old 05-15-2019, 10:42 PM   #50
Rubi513
Pope & Young
 
Rubi513's Avatar
 
Join Date: Aug 2013
Location: Centerville
Hunt In: Walker County
Default

Quote:
Originally Posted by WTucker View Post
Being in the same ditch won’t matter. The conduit will probably end up with water in it anyway.
Yep.
Rubi513 is offline   Reply With Quote Back To The Top
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 01:38 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2019, vBulletin Solutions Inc.
Copyright 1999-2012, TexasBowhunter.com