    Parents ac is blowing hot air from the vents

    They said the fan is running but the air out of the vent is hot. Where should I start looking for the problem

    #2
    Walk outside and see if the condenser fan is turning and the compressor is running

    Comment


      #3
      The fan is running not sure about the compressor. I’m at a wedding so dang the luck

      Comment


        #4
        May be froze up. Shot it off for an hour or so.

        Comment


          #5
          Originally posted by Walker View Post
          May be froze up. Shot it off for an hour or so.
          This^^^ Check condenser inside. If iced over turn ac off and go to fan only for a bit.

          Comment


            #6
            Mine did this when the condensation line was clogged. If that’s it get an air compressor or a shop vac to clear the line. Pain in the butt

            Comment


              #7
              Yup, turn off & check to see if the secondary drain is flowing as well...change filter if dirty.

              Comment


                #8
                Call the AC folks!

                Comment


                  #9
                  Check filters!

                  Comment


                    #10
                    Had the same problem last year and it was some kind of switch/capacitor that kicks the compressor on

                    Outside fan was running but nothing moving in the lines.
                    Stayed semi cool for the couple of days it took to get part

                    Comment


                      #11
                      Originally posted by doghouse View Post
                      This^^^ Check condenser inside. If iced over turn ac off and go to fan only for a bit.
                      Then clean the coils with a shop vac

                      Comment


                        #12
                        Check the float valve. If the drain line is plugged the water backs up and the float valve cuts off the compressor to avoid flooding.

                        Comment


                          #13
                          [ame="https://m.youtube.com/watch?v=AiBFL-l0uxY"]Air Conditioner Not Cooling: Float Switches and Drain Pipe Clogs - YouTube[/ame]

                          Comment


                            #14
                            Originally posted by joevillars View Post
                            The fan is running not sure about the compressor. I’m at a wedding so dang the luck
                            '
                            You're at a wedding. Book a hotel or have them drive to your house.

                            Fix this tomorrow if you can, or Monday with an AC repair man

                            Comment


                              #15
                              If the compressor isn't running, check the capacitor. If it is swollen (bulging out on the sides) that's probably the problem. It's usually a less than $50 part and easy to replace. Getting one might be another story....

                              Sent from my SM-N970U using Tapatalk

                              Comment