Default Federal pacific breaker old box?

Have a old 150 amp panel and looking to add a 30amp double for a stackable
Anyone know what newer style breakers will fit in this
I found these style breaker only used on ebay..
Attached Images
 
kingranch is offline   Reply With Quote Back To The Top
Old 05-26-2022, 06:54 PM   #2
kingranch
Ten Point
 
kingranch's Avatar
 
Join Date: Dec 2010
Location: lakeway
Default

https://www.amazon.com/American-Fede.../dp/B000WUN12C

Will this one pop into the old box?

150$ is alot but rather get a new one
kingranch is offline   Reply With Quote Back To The Top
Old 05-26-2022, 07:04 PM   #3
buckerup
Ten Point
 
Join Date: Feb 2015
Location: Cypress Tx
Hunt In: Gouldbusk, Texas. Coleman County
Default

I have 1, possibly 2 complete panels with all the breakers. Let me look tomorrow and see exactly what I have and then I’ll get back to you.
buckerup is offline   Reply With Quote Back To The Top
Old 05-26-2022, 07:05 PM   #4
waterdog
Pope & Young
 
Join Date: Oct 2006
Default

go look on ebay they have FPE Federal Pacific NA230 Stab Lok 30 Amp 2 Pole Circuit Breaker for $24. 99
waterdog is offline   Reply With Quote Back To The Top
Old 05-26-2022, 07:12 PM   #5
kingranch
Ten Point
 
kingranch's Avatar
 
Join Date: Dec 2010
Location: lakeway
Default

Quote:
Originally Posted by buckerup View Post
I have 1, possibly 2 complete panels with all the breakers. Let me look tomorrow and see exactly what I have and then Iíll get back to you.
Lmk
kingranch is offline   Reply With Quote Back To The Top
Old 05-26-2022, 07:18 PM   #6
Capt.Brown
Ten Point
 
Capt.Brown's Avatar
 
Join Date: Feb 2013
Location: Burnet
Hunt In: Texas
Default

Those are very dangerous breakers I’ve been told by numerous electricians. They sometimes don’t trip and cause fires from what I understand.
Capt.Brown is offline   Reply With Quote Back To The Top
Old 05-26-2022, 07:21 PM   #7
waterdog
Pope & Young
 
Join Date: Oct 2006
Default

Quote:
Originally Posted by Capt.Brown View Post
Those are very dangerous breakers Iíve been told by numerous electricians. They sometimes donít trip and cause fires from what I understand.
^^^^^ this is very true.
waterdog is offline   Reply With Quote Back To The Top
Old 05-26-2022, 07:41 PM   #8
kingranch
Ten Point
 
kingranch's Avatar
 
Join Date: Dec 2010
Location: lakeway
Default

From what I read the breakers themselves are the culprits
Don't they make newer ones to fit?? That are safer designed
kingranch is offline   Reply With Quote Back To The Top
Old 05-26-2022, 07:42 PM   #9
60 Deluxe
Ten Point
 
60 Deluxe's Avatar
 
Join Date: Sep 2012
Location: Coke County
Hunt In: at home
Default

Junk, according to the insurance companies. I had a rental with one in it. Pull out a double thirty and put in a double fifty. I'm sure that it is still in my parts box and I have no use for it. If you get in a pinch, pm me.
60 Deluxe is offline   Reply With Quote Back To The Top
Old 05-26-2022, 08:05 PM   #10
TeamAmerica
Ten Point
 
TeamAmerica's Avatar
 
Join Date: Oct 2016
Location: Dallas
Hunt In: Corsicana (Navarro County)
Default

I have replaced two of these at the advice of professional electricians. Don't know about new breakers that may be compatible.
TeamAmerica is offline   Reply With Quote Back To The Top
Old 05-26-2022, 08:21 PM   #11
1longshot
Eight Point
 
1longshot's Avatar
 
Join Date: Dec 2019
Location: Gonzales,Tx
Hunt In: Gonzales and Lavaca Counties
Default

Connecticut Electric breaker. These are the newer type breaker for old FPE panels, they're grey in color.
1longshot is offline   Reply With Quote Back To The Top
Old 05-26-2022, 11:34 PM   #12
kingranch
Ten Point
 
kingranch's Avatar
 
Join Date: Dec 2010
Location: lakeway
Default

Quote:
Originally Posted by 1longshot View Post
Connecticut Electric breaker. These are the newer type breaker for old FPE panels, they're grey in color.
Thank you longshot!

Just what I was looking for
kingranch is offline   Reply With Quote Back To The Top
Old 05-27-2022, 09:47 AM   #13
bowhntrmatt
Pope & Young
 
bowhntrmatt's Avatar
 
Join Date: Dec 2009
Location: Wimberley
Hunt In: Comstock
Default

Please replace that panel. They lost their UL listing like 30+ years ago.
bowhntrmatt is offline   Reply With Quote Back To The Top
Old 05-27-2022, 09:56 AM   #14
Roman AB
Eight Point
 
Join Date: Nov 2012
Location: Pasadena
Hunt In: Polk County
Default

You can buy them on amazon as well.
Roman AB is offline   Reply With Quote Back To The Top
Old 05-27-2022, 10:05 AM   #15
S-3 Ranch
Pope & Young
 
S-3 Ranch's Avatar
 
Join Date: Jan 2017
Location: Sisterdale
Hunt In: Sisterdale, Barnhart , presidio , tiviolie
Default

Quote:
Originally Posted by bowhntrmatt View Post
Please replace that panel. They lost their UL listing like 30+ years ago.
We have them in our house and it weighs heavy on my mind that
As a retired couple, wife and I can’t afford to replace them anytime soon
The electric contractor quote was outrageously expensive
S-3 Ranch is offline   Reply With Quote Back To The Top
Old 05-27-2022, 10:21 AM   #16
Uncle Saggy
Pope & Young
 
Uncle Saggy's Avatar
 
Join Date: May 2009
Default

Quote:
Originally Posted by Capt.Brown View Post
Those are very dangerous breakers Iíve been told by numerous electricians. They sometimes donít trip and cause fires from what I understand.

So very true
And donít reset an FPE Starter unless your behind a blast shield

That panel needs an upgrade


Sent from my iPhone using Tapatalk
Uncle Saggy is offline   Reply With Quote Back To The Top
Old 05-27-2022, 01:03 PM   #17
chopsknives
Associate Sponsor
 
chopsknives's Avatar
 
Join Date: Sep 2011
Location: Lake Bob Sandlin, Northeast Texas
Default

When I was an electrician for Sanger Harris we would short a circuit out to find the breaker as they never labeled them. The store's that had FPE breakers we could actually leave a nice weld bead around the faceplate and rattle the conduit before they would trip!! If it were me I'd go to another brand rather than risk electrocution or a fire - Just my 2 cents
chopsknives is offline   Reply With Quote Back To The Top
Old 05-27-2022, 01:18 PM   #18
hpdrifter
Ten Point
 
Join Date: Sep 2014
Location: kerens
Hunt In: anywhere I can
Default

I've been out of the business for quite a few years.
Last I heard FPE was a fire hazard just like aluminum wiring. However, my years of absence prevented me from commenting earlier.
If new breakers are available and are UL listed, why change the whole panel?

I'd certainly, replace all the breakers, even if I had to do it one at a time.
hpdrifter is offline   Reply With Quote Back To The Top
Old 05-27-2022, 04:00 PM   #19
sticknstring
Ten Point
 
sticknstring's Avatar
 
Join Date: Oct 2006
Location: South Annetta
Hunt In: searching atm
Default

Federal pacific is bad news. You have a good reason to put in a new panel and add the needed breakers. Jeapardizing your home to fire hazard is just not worth it.
sticknstring is offline   Reply With Quote Back To The Top
Old 05-27-2022, 04:28 PM   #20
Redfeathers
Six Point
 
Redfeathers's Avatar
 
Join Date: Oct 2019
Location: Tom Green County
Default

^^This all the way!!
Redfeathers is offline   Reply With Quote Back To The Top
Old 05-27-2022, 07:12 PM   #21
black42
Ten Point
 
black42's Avatar
 
Join Date: Oct 2011
Location: Alpharetta,GA
Hunt In: Where ever I can
Default

My son in law is a master electrician and he said its like having a welder on the side of your house.
black42 is offline   Reply With Quote Back To The Top
Old 05-28-2022, 12:57 PM   #22
db@100
Ten Point
 
db@100's Avatar
 
Join Date: Sep 2009
Default

Quote:
Originally Posted by hpdrifter View Post
I've been out of the business for quite a few years.
Last I heard FPE was a fire hazard just like aluminum wiring. However, my years of absence prevented me from commenting earlier.
If new breakers are available and are UL listed, why change the whole panel?

I'd certainly, replace all the breakers, even if I had to do it one at a time.
THIS... Now with that said, replacing all the breakers would be expensive also.
db@100 is offline   Reply With Quote Back To The Top
Old 05-28-2022, 01:16 PM   #23
Tony Pic
Pope & Young
 
Tony Pic's Avatar
 
Join Date: Feb 2013
Location: Texas and NYS
Hunt In: The Picarosas North and South, Kerrville, Mountain Home and Harper
Default

I agree with all that you should replace the federal pacific panel. We called them no blow Federals. Maybe the new breakers are built differently, but the original FP breakers are known not to trip. If you can change your panel, by all means. Do it.
Tony Pic is offline   Reply With Quote Back To The Top
Old 05-28-2022, 03:34 PM   #24
Mountaineer
Eight Point
 
Mountaineer's Avatar
 
Join Date: Aug 2010
Location: McKinney
Hunt In: WV,SD, Hunt co
Default

Replace the entire panel. Itís past itís useful lifetime and the breakers are a known hazard.

https://inspectapedia.com/fpe/FPE_Stab_Lok_Hazards.php


Sent from my iPhone using Tapatalk
Mountaineer is offline   Reply With Quote Back To The Top
Old 05-28-2022, 11:06 PM   #25
Big_gun
Ten Point
 
Big_gun's Avatar
 
Join Date: Oct 2006
Location: Wallis
Hunt In: Llano
Default

For the cost of new replacement breakers you can replace the panel with newer breakers. If your handy itís not that hard.


Sent from my iPhone using Tapatalk Pro
Big_gun is offline   Reply With Quote Back To The Top
Old 05-28-2022, 11:28 PM   #26
Redfeathers
Six Point
 
Redfeathers's Avatar
 
Join Date: Oct 2019
Location: Tom Green County
Default

Some insurance companies will not insurance the building with that panel.
Redfeathers is offline   Reply With Quote Back To The Top
Old 05-28-2022, 11:31 PM   #27
kingranch
Ten Point
 
kingranch's Avatar
 
Join Date: Dec 2010
Location: lakeway
Default

I can get all new updated CE breakers for 250$

Can someone explain what part the panel itself plays in this hazard.. from what I can figure the breakers where the weak link-
kingranch is offline   Reply With Quote Back To The Top
Old 05-29-2022, 12:24 AM   #28
Redfeathers
Six Point
 
Redfeathers's Avatar
 
Join Date: Oct 2019
Location: Tom Green County
Default

Do a quick google search and you will find plenty to read and testing data. One of the first searches that came up was insurance companies not insuring these panels. If I remember right, a lot of the panels were installed from the 50’s to 85, with some being just a tad later.
Redfeathers is offline   Reply With Quote Back To The Top
Old 05-29-2022, 07:02 AM   #29
db@100
Ten Point
 
db@100's Avatar
 
Join Date: Sep 2009
Default

Quote:
Originally Posted by kingranch View Post
I can get all new updated CE breakers for 250$

Can someone explain what part the panel itself plays in this hazard.. from what I can figure the breakers where the weak link-
If the breakers you are buying are UL listed, then you should be safe. You may still have to argue with people because the panel is a "FPE" panel.
db@100 is offline   Reply With Quote Back To The Top
Old 05-29-2022, 08:50 AM   #30
kingranch
Ten Point
 
kingranch's Avatar
 
Join Date: Dec 2010
Location: lakeway
Default

https://www.cpsc.gov/Newsroom/News-R...-For-Consumers


I'd replace everything however this current panel acts as a pass through for another unit in the complex. That would mean paying a contractor/electrician to enter another person's unit to disconnect their feed and run it out from my box. Very strange setup imo. I figured the safest and easiest way to correct all of this is new CE UL listed breakers that are stablok
kingranch is offline   Reply With Quote Back To The Top
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 02:13 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2022, vBulletin Solutions Inc.
Copyright 1999-2012, TexasBowhunter.com