    Generator / electric panel question

    Hi all, I'm looking to hook up a portable generator in case of emergency. As seen in the picture, the panel under the meter is feeding a 200 amp service underground to another panel inside the house. (About 100 feet away behind me)

    My question is can I install the generator power inlet to this panel? (The house panel is out of slots)

    Click image for larger version

Name:	20210606_121912.jpg
Views:	1
Size:	141.4 KB
ID:	25251302

    #2
    Yes. Need manual transfer switch or panel interlock to do it properly.

    Comment


      #3
      Yes, as long as you have a MCB in that panel.

      Comment


        #4
        A manual interlock device should be mounted just below the main breaker.

        Comment


          #5
          Originally posted by Rubi513 View Post
          Yes, as long as you have a MCB in that panel.
          How do I tell? I attached a pic on the panel door.Click image for larger version

Name:	20210607_083734.jpg
Views:	1
Size:	102.8 KB
ID:	24653496

          Comment


            #6
            Originally posted by etxranch View Post
            How do I tell? I attached a pic on the panel door.[ATTACH]1051986[/ATTACH]
            My fault with the abbreviation.
            Do you have a main circuit breaker?
            If so, you would need the interlock kit that has been mentioned.

            Comment


              #7
              I've been thinking of doing this for my house. I had an electrician give me a quote for over $2000! I about fell out. I definitely don't want to back feed the circuit and I'm not much of an electrician. That just seemed out of control on pricing

              Comment


                #8
                Originally posted by elhefe View Post
                I've been thinking of doing this for my house. I had an electrician give me a quote for over $2000! I about fell out. I definitely don't want to back feed the circuit and I'm not much of an electrician. That just seemed out of control on pricing
                If you have space in your panel and can move things around enough to install a two pole breaker in the top right position it should be fairly straight forward.

                Comment


                  #9
                  Originally posted by elhefe View Post
                  I've been thinking of doing this for my house. I had an electrician give me a quote for over $2000! I about fell out. I definitely don't want to back feed the circuit and I'm not much of an electrician. That just seemed out of control on pricing
                  That's lots of money, but if you are unfamiliar with electricity and have to rewire lots of breakers then it might be worth the cost. Here is a video about how the power inlet is done:

                  Last edited by etxranch; 06-07-2021, 11:08 AM.

                  Comment


                    #10
                    Speaking from an electrical contractor perspective, material costs are through the roof right now. Aluminum wire is up 50-60% and copper is up 90-100%. And labor certainly isn’t getting any cheaper.


                    Sent from my iPhone using Tapatalk Pro

                    Comment


                      #11
                      I bought the interlock switch and did it my self for around 100 bucks

                      Comment


                        #12
                        i just did this, it cost like 100$
                        the most expensive was the #6 wire from home depot was like 40$ for just a few feet for the whip

                        Comment


                          #13
                          Originally posted by Mike D View Post
                          Speaking from an electrical contractor perspective, material costs are through the roof right now. Aluminum wire is up 50-60% and copper is up 90-100%. And labor certainly isn’t getting any cheaper.


                          Sent from my iPhone using Tapatalk Pro
                          Hope they come down soon. Just saw lumber dropped a little for the first time in months.

                          Comment


                            #14
                            Yes you can. Just got mine done to my house. Use a lic. elect. Most places require you get a permit and the power company might come out and pull the meter pan till switch is installed. I know what some are saying on here and I was told the same thing. But a lic. elect. and a good friend told no way. Do it right cause if some thing wrong you will be in a heep of trouble. Cost me $2300 because I waited so long and some of that stuff is hard to fine not even you can get it and the prices of material are going up every dad. My biggest cost was for my feed wire from generator to the switch box that was 85' but I wanted generator away from my house in my shed and made it a extra longer just in case. You might not have that problem looking at your pictures. Do not try to run power from your gen. to a dryer plug end people do that but God for bid if some happens and some one gets kill or you burn your house down. Cause if happens they will come check it. Good Luck but If I was you I would get it done by a lic. person Brother

                            Comment


                              #15
                              Yep

                              Originally posted by RSMDTX View Post
                              Yes. Need manual transfer switch or panel interlock to do it properly.
                              This
                              Attached Files
                              Last edited by JFFB; 06-07-2021, 12:54 PM. Reason: adding picture

                              Comment