Question for the TBH electricians
Collapse
X
-
Had a guy(not on TBH) tell that I could run 3/0 triplex and put in a ground rod to the sub panel.
I plan on putting in a ground rod at the sub panel regardless, but is that something that could be done, but not advisable.
I figure to use a ground rod at the well house as well. Will meet with PEC engineer this week. Should have my exact distances then.
Comment
-
Originally posted by FLASH_OUTDOORS View PostMeter to shop I would run 2/2/4/6 AL in 1 1/4” pvc
Meter to well house I would run 8/8/10/12 CU in 3/4” pvc
Meter to house I would run 4/0, 4/0, 2/0, #4 AL 2” pvc
Sent from my iPhone using Tapatalk Pro
Comment
-
Originally posted by Huntindad View Postare those individual wires ? or is there a name to use if I go to say...Elliot ectrical supply.
Individual wires, but they can be bought bundled ^^
The #2 are your hots, the #4 is your neutral, and #6 is your ground.
Comment
-
Originally posted by Huntindad View Postsweet, good to know that combo comes bundled.
thanx folks.
Tell Elliot you want 2/2/4 URD. And a separate #6 AL. That’s how you will need to buy. PM me and I will call in the order under my account and have whatever you need ready waiting in will call. You will need to pay of course[emoji12]