    Originally posted by Mark116 View Post
    Do what Flash is saying.

    Anything that feeds a sub panel has to have 4 wires.

    you can down size the neut one size.

    My house has a 200 amp feed through panel on a pole. about a 100 foot to the house. came off that panel with 100 amps to the shop
    You can downsize more than one size. Especially if you can show load calculations.

    Comment


      #32
      Had a guy(not on TBH) tell that I could run 3/0 triplex and put in a ground rod to the sub panel.

      I plan on putting in a ground rod at the sub panel regardless, but is that something that could be done, but not advisable.

      I figure to use a ground rod at the well house as well. Will meet with PEC engineer this week. Should have my exact distances then.

      Comment


        #33
        If it's a subpanel outside the main building, then yes you need a ground rod, 2 hots, a neutral and ground coming from the main panel.

        Comment


          #34
          Originally posted by FLASH_OUTDOORS View Post
          Meter to shop I would run 2/2/4/6 AL in 1 1/4” pvc
          Meter to well house I would run 8/8/10/12 CU in 3/4” pvc
          Meter to house I would run 4/0, 4/0, 2/0, #4 AL 2” pvc


          Sent from my iPhone using Tapatalk Pro
          are those individual wires ? or is there a name to use if I go to say...Elliot ectrical supply.

          Comment


            #35
            Originally posted by Huntindad View Post
            are those individual wires ? or is there a name to use if I go to say...Elliot ectrical supply.


            Individual wires, but they can be bought bundled ^^
            The #2 are your hots, the #4 is your neutral, and #6 is your ground.

            Comment


              #36
              sweet, good to know that combo comes bundled.

              thanx folks.

              Comment


                #37
                Originally posted by Huntindad View Post
                sweet, good to know that combo comes bundled.

                thanx folks.

                Tell Elliot you want 2/2/4 URD. And a separate #6 AL. That’s how you will need to buy. PM me and I will call in the order under my account and have whatever you need ready waiting in will call. You will need to pay of course[emoji12]