Need help, I want to run power to one of my sheds I have a 125 amp box and about 750' of #6 wire. I need to run it about 123' I was told that I would be able to draw no more than 50 Amps at that distance. One guy told me that I can run 5 wires, 2 for hot, 2 for neutral and 1 ground to increase the amps. I don't anything about that any help thanks.
Announcement
Collapse
No announcement yet.
Electrician Help
Collapse
X
-
What are you planning on running out there in shed. Welder, power tools, lights,etc That'll make a big difference. If you plan on using just the #6 and don't want to buy wire then a Double Pole 50amp breaker in main panel and a main lug panel in shed will work fine at that distance, but it may limit what you can do based on what you're running out there.
Comment
-
Originally posted by splitbeam145 View PostWhat are you planning on running out there in shed. Welder, power tools, lights,etc That'll make a big difference. If you plan on using just the #6 and don't want to buy wire then a Double Pole 50amp breaker in main panel and a main lug panel in shed will work fine at that distance, but it may limit what you can do based on what you're running out there.
Comment
-
Originally posted by bowhunt3 View PostNeed help, I want to run power to one of my sheds I have a 125 amp box and about 750' of #6 wire. I need to run it about 123' I was told that I would be able to draw no more than 50 Amps at that distance. One guy told me that I can run 5 wires, 2 for hot, 2 for neutral and 1 ground to increase the amps. I don't anything about that any help thanks.
What type of wire is it? Is it romex? Thhn? UF? If it's single conductor thhn you can run 3 #6's and a #10 for the ground. If all you have is #6 then use that. Make sure the grounds and neutrals are separated and the bonding screw is out. Set a ground rod at your shop. Run a wire from your sub panel to the ground rod.
Comment
-
Originally posted by FLASH_OUTDOORS View PostWhat type of wire is it? Is it romex? Thhn? UF? If it's single conductor thhn you can run 3 #6's and a #10 for the ground. If all you have is #6 then use that. Make sure the grounds and neutrals are separated and the bonding screw is out. Set a ground rod at your shop. Run a wire from your sub panel to the ground rod.