    #16
    no one has mentioned the distance. 12 AWG wire will carry 20 amps but only to a distance of 50'. beyond that the amp loss requires a 10AWG wire.

    one way distance always is part of the calculation. there are calculators on the WWW to help you.

    Comment


      #17
      Originally posted by cvanbrunt View Post
      I always try to put them on dedicated circuits to make sure nothing else trips the breaker and kills the power to the fridge or deep freezer.


      Sent from my iPhone using Tapatalk
      x's 2

      Comment


        #18
        12/2 Romex yellow with bare copper ground and never look back. You can safely run 1800 watts on a 20a circuit and 12/2 Romex NM-B. Am assuming you are not running in conduit.

        Comment


          #19
          Originally posted by Mike D View Post
          Circuit size is up to you (15 or 20A). If it were mine the fridge receptacle would be a 20A dedicated circuit.

          The rest I would just do typical 15A circuits.

          12/2 Romex for the 20A and 14/2 Romex for the 15A ones.


          Sent from my iPhone using Tapatalk Pro
          ^^^^^ Yep this is what I would do.