What am I missing here?

I added this panel to my shop several months ago... only the odd 1, 3, 5 spaces have juice.

please be gentle... I am NOT an electrician by an stretch of the imagination.

Name:  20180210_180433.jpg
Views: 511
Size:  97.0 KB
JFISHER is offline   Reply With Quote Back To The Top
Old 02-10-2018, 07:39 PM   #2
125Dad
Pope & Young
 
125Dad's Avatar
 
Join Date: Aug 2010
Location: keller
Hunt In: Coke Co.
Default

You only took 110 to the panel.
One hot
One neutral

You need another hot for the lug on the far right.
125Dad is offline   Reply With Quote Back To The Top
Old 02-10-2018, 07:40 PM   #3
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: for a lease
Default

Oh my! So many things wrong here!

The white neutral wire coming out of the back of sub panel is terminated in the wrong spot. This should go where your black wire is terminated. Your black wire coming out the back of panel should be landed on the far right lug. Your ground should be made up but not bonded if this is a sub panel.

Whatís unknown is the breaker thatís feeding this panel. Is it a single pole or two pole breaker?? I would not plug anything in you care about until this is fixed.

Last edited by Electrican; 02-10-2018 at 07:46 PM.
Electrican is offline   Reply With Quote Back To The Top
Old 02-10-2018, 07:42 PM   #4
125Dad
Pope & Young
 
125Dad's Avatar
 
Join Date: Aug 2010
Location: keller
Hunt In: Coke Co.
Default

There is a lot of issues in that panel by the way.

In my opinion very unsafe
125Dad is offline   Reply With Quote Back To The Top
Old 02-10-2018, 07:43 PM   #5
sendit
Ten Point
 
sendit's Avatar
 
Join Date: May 2016
Default

Oh my x 2
sendit is offline   Reply With Quote Back To The Top
Old 02-10-2018, 07:44 PM   #6
125Dad
Pope & Young
 
125Dad's Avatar
 
Join Date: Aug 2010
Location: keller
Hunt In: Coke Co.
Default

Quote:
Originally Posted by Electrican View Post
Oh my! So many things wrong here!
Just like your avatar picture.
125Dad is offline   Reply With Quote Back To The Top
Old 02-10-2018, 07:44 PM   #7
systemnt
Pope & Young
 
systemnt's Avatar
 
Join Date: Aug 2009
Location: Montgomery
Hunt In: South Texas
Default

Obama thinks thats a clock.
systemnt is offline   Reply With Quote Back To The Top
Old 02-10-2018, 07:47 PM   #8
TxTechBowhunter
Ten Point
 
TxTechBowhunter's Avatar
 
Join Date: Oct 2006
Location: Parker County
Hunt In: Brewster, Cooke and Clay County
Default

Is that a hot leg hooked up to the neutral bar? And and a neutral hooked to the bus? Please call an electrician..
TxTechBowhunter is offline   Reply With Quote Back To The Top
Old 02-10-2018, 07:48 PM   #9
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: for a lease
Default

Quote:
Originally Posted by 125Dad View Post
Just like your avatar picture.
The best! Really hope you arenít the other major brand fan boy.
Electrican is offline   Reply With Quote Back To The Top
Old 02-10-2018, 07:50 PM   #10
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: for a lease
Default

Serous question here. Does any of the plugs actually work??
Electrican is offline   Reply With Quote Back To The Top
Old 02-10-2018, 07:52 PM   #11
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: for a lease
Default

Oh and I might or might not have saved this pic for future use. Lol
Electrican is offline   Reply With Quote Back To The Top
Old 02-10-2018, 07:54 PM   #12
TeamAmerica
Eight Point
 
TeamAmerica's Avatar
 
Join Date: Oct 2016
Location: Dallas
Hunt In: Corsicana (Navarro County)
Default

Stop what you are doing!
TeamAmerica is offline   Reply With Quote Back To The Top
Old 02-10-2018, 07:57 PM   #13
panhandlehunter
Pope & Young
 
panhandlehunter's Avatar
 
Join Date: Sep 2010
Location: Sweeny
Hunt In: Brazoria, Matagorda & Kinney Counties
Default

You need to kill the power to it and then call an electrician.
panhandlehunter is online now   Reply With Quote Back To The Top
Old 02-10-2018, 08:02 PM   #14
125Dad
Pope & Young
 
125Dad's Avatar
 
Join Date: Aug 2010
Location: keller
Hunt In: Coke Co.
Default

Quote:
Originally Posted by Electrican View Post
The best! Really hope you arenít the other major brand fan boy.
Iím a ďPRIMEĒ fan.
125Dad is offline   Reply With Quote Back To The Top
Old 02-10-2018, 08:03 PM   #15
JFISHER
Pope & Young
 
JFISHER's Avatar
 
Join Date: Jan 2008
Location: Brownwood
Hunt In: BWD
Default

Quote:
Originally Posted by Electrican View Post
Serous question here. Does any of the plugs actually work??
Yeah everything works lol

I think the main confusion here are the wire color mismatch.

Yes this is a sub panel.

Coming from the main at the house it starts as 3 wire red, white, black from a 30 amp 2 pole.

Prior to my running this out to the shop, this circuit used to terminate at an old 240 window unit AC or swamp cooler. (old house)

Since I wasn't going to use either of those I decided to run it out to my shop for lights and a few outlets. Over the passed few years I decided it was time to dump the 1950'e fuse box that was out there.

If I recall, what is "running out to the panel" now is one leg of that 30 on the main and neutral. The original red leg is simply wire nutted off, taped and inside a junction box, as I only have 10/2 (with ground) between the main and shop panel.


Should I ditch the 2 pole at the main breaker or run the 3 wire (red/black) all the way out there? I don't have anything out there that requires 240.
JFISHER is offline   Reply With Quote Back To The Top
Old 02-10-2018, 08:09 PM   #16
JFISHER
Pope & Young
 
JFISHER's Avatar
 
Join Date: Jan 2008
Location: Brownwood
Hunt In: BWD
Default

Quote:
Originally Posted by Electrican View Post
Oh and I might or might not have saved this pic for future use. Lol
LMAO... you wouldn't believe what I did to determine "which wire should I use "

I basically hooked the shop end wire to my the (rest in peace) shop vac.... and turned it on so I'd be able to hear it and know there was juice flowing...turned off the 2 pole breaker at the house, then started twisting wires. Flipped the breaker... Cool! shop vac obviously running.

Started walking out there... then saw the smoke. Ran back and flipped the breaker. That's when I think I realized that this was a 240 circuit.

SO I basically eliminated one side of it... then used the same process of elimination (meaning, no fires or sparks yet) process to reconnect to the new sub panel.


This IS the DIY thread right
JFISHER is offline   Reply With Quote Back To The Top
Old 02-10-2018, 08:12 PM   #17
JFISHER
Pope & Young
 
JFISHER's Avatar
 
Join Date: Jan 2008
Location: Brownwood
Hunt In: BWD
Default

This is what's at the house end...

leading to the shop

Name:  house.jpg
Views: 454
Size:  70.4 KB

Last edited by JFISHER; 02-10-2018 at 08:30 PM.
JFISHER is offline   Reply With Quote Back To The Top
Old 02-10-2018, 08:45 PM   #18
Electrican
Pope & Young
 
Electrican's Avatar
 
Join Date: Oct 2011
Location: Burleson TX
Hunt In: for a lease
Lightbulb

Quote:
Originally Posted by JFISHER View Post
LMAO... you wouldn't believe what I did to determine "which wire should I use "

I basically hooked the shop end wire to my the (rest in peace) shop vac.... and turned it on so I'd be able to hear it and know there was juice flowing...turned off the 2 pole breaker at the house, then started twisting wires. Flipped the breaker... Cool! shop vac obviously running.

Started walking out there... then saw the smoke. Ran back and flipped the breaker. That's when I think I realized that this was a 240 circuit.

SO I basically eliminated one side of it... then used the same process of elimination (meaning, no fires or sparks yet) process to reconnect to the new sub panel.


This IS the DIY thread right

Ahh the ole smoke check method. Makes sense now. Lol
Electrican is offline   Reply With Quote Back To The Top
Old 02-10-2018, 08:48 PM   #19
JFISHER
Pope & Young
 
JFISHER's Avatar
 
Join Date: Jan 2008
Location: Brownwood
Hunt In: BWD
Default

Quote:
Originally Posted by Electrican View Post
Ahh the ole smoke check method. Makes sense now. Lol
JFISHER is offline   Reply With Quote Back To The Top
Old 02-10-2018, 08:50 PM   #20
Rubberdown
Eight Point
 
Join Date: May 2015
Location: Houston
Default

Sir... Please call an electrician. I'm not trying to be rude or funny but there is literally nothing right about that panel so far.
Rubberdown is online now   Reply With Quote Back To The Top
Old 02-10-2018, 09:14 PM   #21
RJH1
Eight Point
 
Join Date: Mar 2015
Location: Abilene
Hunt In: Abilene area
Default

Where is the red wire coming from the house, it is not in the other box? Generally speaking white is ground, and black is hot. They seem to be backwards in your sub box. The red and black (both hot) from the house should go on the bars that the breakers hook to, cant remember the technical name (red on one black on the other). The white should go to the ground bar
RJH1 is offline   Reply With Quote Back To The Top
Old 02-10-2018, 09:48 PM   #22
125Dad
Pope & Young
 
125Dad's Avatar
 
Join Date: Aug 2010
Location: keller
Hunt In: Coke Co.
Default

Don’t forget you need to have a isolated ground from your neutral bar.
125Dad is offline   Reply With Quote Back To The Top
Old 02-10-2018, 10:19 PM   #23
sendit
Ten Point
 
sendit's Avatar
 
Join Date: May 2016
Default

Quote:
Originally Posted by 125Dad View Post
Donít forget you need to have a isolated ground from your neutral bar.

It's isolated alright. The ground wire from the romex feeder isn't hooked up to anything and the ground wire(s) have been cut off of the romex on the load side.
sendit is offline   Reply With Quote Back To The Top
Old 02-10-2018, 10:28 PM   #24
WTucker
Six Point
 
WTucker's Avatar
 
Join Date: Aug 2016
Location: Orangefield
Hunt In: Hardin County
Default

You really need to get a qualified electrician out there. Lots wrong here.
WTucker is offline   Reply With Quote Back To The Top
Old 02-10-2018, 10:32 PM   #25
hot_rod_eddie
Ten Point
 
hot_rod_eddie's Avatar
 
Join Date: Aug 2014
Location: North Carolina
Hunt In: NC, SC
Default

Seriously, like the others said - turn off the power and slowly back away. Call an electrician. We can tell you what to do, but considering all the things wrong with that panel, I would be concerned to help you go any further.
hot_rod_eddie is offline   Reply With Quote Back To The Top
Old 02-10-2018, 10:34 PM   #26
silencer2011
Eight Point
 
silencer2011's Avatar
 
Join Date: Dec 2011
Location: Henrietta, TX
Hunt In: Clay County
Default

Please just pay an electrician to come out there.
silencer2011 is offline   Reply With Quote Back To The Top
Old 02-10-2018, 10:46 PM   #27
JFISHER
Pope & Young
 
JFISHER's Avatar
 
Join Date: Jan 2008
Location: Brownwood
Hunt In: BWD
Default

Thanks guys. I appreciate the concerns, really. I've been operating the shop as is with several overhead lights, band saw, table saw, air cleaner, vac system and replying via my shop PC.

I am planning a complete redo from the house to shop, soon as I can get my friend the electrician over for a 6 pack or 2... he likes him some beer

It's been "good enough" while I was just using the shop for storage, but now that I spend 80% of my free time out here, well, time to get it done.
JFISHER is offline   Reply With Quote Back To The Top
Old 02-10-2018, 11:18 PM   #28
hot_rod_eddie
Ten Point
 
hot_rod_eddie's Avatar
 
Join Date: Aug 2014
Location: North Carolina
Hunt In: NC, SC
Default

Okay - Here is how it is supposed to be. White wire is neutral, black is 110v, and red is 110v. Move the black wire to where the white wire is and the white wire to where the black wire is. Connect the bare wire to the green screw. The red wire goes to the big lug on the far right. Without the red wire you will not have power to half of the circuits. I still suggest you get an electrician because if the wiring/house is old or worked on over the years there is no telling what is going on. An electrician will verify the circuit in the main box and each wire going into the new panel. If you can't verify the main panel or have a good knowledge of a voltmeter, it is impossible for us to safely tell you what is right.

Last edited by hot_rod_eddie; 02-10-2018 at 11:23 PM.
hot_rod_eddie is offline   Reply With Quote Back To The Top
Old 02-11-2018, 12:22 AM   #29
hweissert
Ten Point
 
hweissert's Avatar
 
Join Date: Feb 2007
Location: Bonham
Hunt In: Panhandle, Fannin, Grayson, Kansas, Oklahoma
Default

And probably the least of your worries here but 14 awg wire is only good for 15 amps. Probably should shuck the 20 and 30 amp single pole breakers in the sub panel while you’re at it.
hweissert is offline   Reply With Quote Back To The Top
Old 02-11-2018, 03:06 PM   #30
Big_gun
Ten Point
 
Big_gun's Avatar
 
Join Date: Oct 2006
Location: Wallis
Hunt In: Open for Suggestions
Default

I think you best get your electrician a 24 pack.... ;-) of you need the extra circuits I would replace the wire from you j-box with one so that you can get 220v at this panel.
if its not that far replace entire run to the shop. blk and red to the hot lugs and the neutral(white) to the neutral bar and ground the ground bar minus a bod between the ground and neutral bar ( although I do not see a ground bar in this panel. )
Big_gun is offline   Reply With Quote Back To The Top
Old 02-11-2018, 03:45 PM   #31
hot_rod_eddie
Ten Point
 
hot_rod_eddie's Avatar
 
Join Date: Aug 2014
Location: North Carolina
Hunt In: NC, SC
Default

Quote:
Originally Posted by Big_gun View Post
I think you best get your electrician a 24 pack.... ;-) of you need the extra circuits I would replace the wire from you j-box with one so that you can get 220v at this panel.
if its not that far replace entire run to the shop. blk and red to the hot lugs and the neutral(white) to the neutral bar and ground the ground bar minus a bod between the ground and neutral bar ( although I do not see a ground bar in this panel. )
Why would you need a ground bar? All the grounds are snipped off. Sarcasm
hot_rod_eddie is offline   Reply With Quote Back To The Top
Old 02-11-2018, 03:55 PM   #32
Mrsailfish
Four Point
 
Join Date: Jan 2014
Default

You should turn that off and call out an electrician
Mrsailfish is offline   Reply With Quote Back To The Top
Old 02-11-2018, 05:09 PM   #33
db@100
Eight Point
 
db@100's Avatar
 
Join Date: Sep 2009
Default

"I am NOT an electrician by an stretch of the imagination"
I think this is an understatement!
Next time just ask and I'm sure one of us will be glad to help before you or someone else gets hurt.
db@100 is offline   Reply With Quote Back To The Top
Old 02-11-2018, 08:03 PM   #34
JFISHER
Pope & Young
 
JFISHER's Avatar
 
Join Date: Jan 2008
Location: Brownwood
Hunt In: BWD
Default

Quote:
Originally Posted by hot_rod_eddie View Post
Why would you need a ground bar? All the grounds are snipped off. Sarcasm
Bootleg ground
JFISHER is offline   Reply With Quote Back To The Top
Old 02-11-2018, 08:05 PM   #35
JFISHER
Pope & Young
 
JFISHER's Avatar
 
Join Date: Jan 2008
Location: Brownwood
Hunt In: BWD
Default

Quote:
Originally Posted by Big_gun View Post
I think you best get your electrician a 24 pack.... ;-) of you need the extra circuits I would replace the wire from you j-box with one so that you can get 220v at this panel.
if its not that far replace entire run to the shop. blk and red to the hot lugs and the neutral(white) to the neutral bar and ground the ground bar minus a bod between the ground and neutral bar ( although I do not see a ground bar in this panel. )
That's the plan. Rewired what is there today. Tested all outlets, 2 amber all grounded. Polarity, check.

I was also told that since this is basically a sub panel, it wouldn't need it's own separate ground.
JFISHER is offline   Reply With Quote Back To The Top
Old 02-11-2018, 08:12 PM   #36
ttaxidermy
Pope & Young
 
ttaxidermy's Avatar
 
Join Date: Nov 2009
Location: Brazoria county
Hunt In: Brady,McCulloch Cnty, Brazoria cnty, South Africa, Namibia
Default

SLOWLY back away from the Breaker box with your hands above your head..
ttaxidermy is offline   Reply With Quote Back To The Top
Old 02-11-2018, 08:18 PM   #37
WTucker
Six Point
 
WTucker's Avatar
 
Join Date: Aug 2016
Location: Orangefield
Hunt In: Hardin County
Default

You still need a separate ground. It just doesnt get bonded to your neutral. You also have fire hazards with those breakers on 14 awg romex.
WTucker is offline   Reply With Quote Back To The Top
Old 02-11-2018, 08:35 PM   #38
hot_rod_eddie
Ten Point
 
hot_rod_eddie's Avatar
 
Join Date: Aug 2014
Location: North Carolina
Hunt In: NC, SC
Default

The panel still needs a ground. All the copper wires go to a ground bar similar to how all the white wire go one bar. One copper wire goes from the bar back to the main panel. In the main panel the bar for the white wire and the bars for the copper wires are joined together (bonded). You don't bond a subpanel. Like other have said, the wires going to your loads are too small for the breaker size. Therefore you will let the smoke out of the wires before the breakers trip. This defeats the purpose and leads to a fire.
hot_rod_eddie is offline   Reply With Quote Back To The Top
Old 02-11-2018, 08:47 PM   #39
Greenheadless
Ten Point
 
Greenheadless's Avatar
 
Join Date: Dec 2006
Location: Houston, TX
Hunt In: Liberty County
Default

Make sure your insurance is up to date and will cover fire. Also, you can seriously screw up anything of electronics right now.

As others have said, I would kill the breaker and back away until you get someone out there that knows what they are doing.
Greenheadless is offline   Reply With Quote Back To The Top
Old 02-11-2018, 09:43 PM   #40
Zoomaster
Four Point
 
Zoomaster's Avatar
 
Join Date: Nov 2017
Default

Quote:
Originally Posted by systemnt View Post
Obama thinks thats a clock.
Lol

Sent from my XT1650 using Tapatalk
Zoomaster is offline   Reply With Quote Back To The Top
Old 02-12-2018, 06:13 PM   #41
JFISHER
Pope & Young
 
JFISHER's Avatar
 
Join Date: Jan 2008
Location: Brownwood
Hunt In: BWD
Default

As for the wire running from the House (30 amp double pole) do I calculate for each leg separate, or combined... meaning, 12 gauge for 15 amps each or 10 for the combined 30?
JFISHER is offline   Reply With Quote Back To The Top
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:07 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2018, vBulletin Solutions Inc.
Copyright 1999-2012, TexasBowhunter.com