Default School me on arc fault breakers

Required on new builds? All rooms in the house? Just bedrooms? ect.
pyrobow is offline   Reply With Quote Back To The Top
Old 04-16-2018, 04:09 PM   #2
Dale Moser
Pope & Young
 
Dale Moser's Avatar
 
Join Date: Oct 2006
Location: Wise Cty
Hunt In: Young Cty
Default

They are trash. I replaced some of them with real breakers in our house.

Static from your finger to the switch can trip them. All kinds of stuff trips them.


Sent from my iPhone using Tapatalk
Dale Moser is offline   Reply With Quote Back To The Top
Old 04-16-2018, 04:18 PM   #3
Mrsailfish
Four Point
 
Join Date: Jan 2014
Default

Unless you have to have these for inspection, do not get them unless you want to be resetting breakers. I have seen ceiling fans, printers, TVs trip them for no reason.
Mrsailfish is offline   Reply With Quote Back To The Top
Old 04-16-2018, 04:19 PM   #4
meltingfeather
Ten Point
 
Join Date: Oct 2012
Location: austin
Hunt In: Gillespie, San Saba & Kerr primarily
Default

they are worthless... and required basically everywhere.
Killer combo
meltingfeather is offline   Reply With Quote Back To The Top
Old 04-16-2018, 04:21 PM   #5
justintyme8303
Pope & Young
 
justintyme8303's Avatar
 
Join Date: Feb 2009
Location: The Great State
Hunt In: Any
Default

Quote:
Originally Posted by Mrsailfish View Post
Unless you have to have these for inspection, do not get them unless you want to be resetting breakers. I have seen ceiling fans, printers, TVs trip them for no reason.
X2

we have 1 plug that we cant plug the vacuum cleaner to. If we do when you push the button to stop the brushes to go from carpet to hardwood it trips.
justintyme8303 is offline   Reply With Quote Back To The Top
Old 04-16-2018, 06:06 PM   #6
bloodtrailer28
Pope & Young
 
Join Date: Jul 2014
Location: Oatmeal, TX
Default

Trash. You won't be getting inspected in burner co so no need to worry about them.
bloodtrailer28 is offline   Reply With Quote Back To The Top
Old 04-16-2018, 06:18 PM   #7
jrfan
Ten Point
 
jrfan's Avatar
 
Join Date: Jun 2008
Location: Wills Point/lake Tawakoni
Hunt In: Callahan co.
Default

They can be a pain in the butt like smoke alarms until you need them to save your house or your life. Then they are the greatest thing since sliced bread.
jrfan is offline   Reply With Quote Back To The Top
Old 04-16-2018, 06:45 PM   #8
FLASH_OUTDOORS
Ten Point
 
FLASH_OUTDOORS's Avatar
 
Join Date: Aug 2012
Location: Tomball
Hunt In: Kennard
Default

The worst things invented other than ďthe windiĒ



Sent from my iPhone using Tapatalk
FLASH_OUTDOORS is offline   Reply With Quote Back To The Top
Old 04-16-2018, 08:38 PM   #9
mattjproc
Six Point
 
Join Date: Oct 2009
Location: Cedar Park
Hunt In: Llano
Default

For sure. Pure junk.
mattjproc is offline   Reply With Quote Back To The Top
Old 04-16-2018, 08:49 PM   #10
Mountaineer
Six Point
 
Mountaineer's Avatar
 
Join Date: Aug 2010
Location: McKinney
Hunt In: WV,SD, Hunt co
Default

Texas adopted the 2017 NEC in September, so technically required but who enforces it? Municipalities will differ on code cycle and outside city limits it's a 'do whatever you want' in many areas.

In the 2017 edition of the NECģ, Section 210.12 requires that for dwelling units, all 120-volt, single-phase, 15- and 20-ampere branch circuits supplying outlets or devices installed in dwelling unit kitchens, family rooms, dining rooms, living rooms, parlors, libraries, dens, bedrooms, sunrooms, recreation rooms, closets, hallways, laundry areas, or similar rooms or areas shall be protected by AFCIs.
Mountaineer is offline   Reply With Quote Back To The Top
Old 04-16-2018, 08:55 PM   #11
txtradesman
Ten Point
 
txtradesman's Avatar
 
Join Date: Aug 2009
Location: Austin
Hunt In: Texas
Default

from what Ive gathered.. and Im a Journeyman Electrician

motors trip them the most..

ceiling fans, blenders, vacuums, and etc

Ive been servicing them for several years
txtradesman is offline   Reply With Quote Back To The Top
Old 04-16-2018, 10:22 PM   #12
Low Fence
Pope & Young
 
Low Fence's Avatar
 
Join Date: Aug 2008
Location: Quitman, Tx.
Default

I hope whoever mandated them is one day put on a respirator... that’s plugged into one. I despise them
Low Fence is offline   Reply With Quote Back To The Top
Old 04-16-2018, 10:51 PM   #13
BigThicketBoy
Pope & Young
 
BigThicketBoy's Avatar
 
Join Date: Aug 2011
Location: Barbers Hill Tx
Hunt In: Hardin Co
Default

Do not put them on anything that you want to stay cold. The lights blink and they trip and you don't notice it you lose three deers worth of meat. Ask me how I know

Sent from my Moto Z (2) using Tapatalk
BigThicketBoy is offline   Reply With Quote Back To The Top
Old 04-17-2018, 06:09 AM   #14
AgHntr10
Pope & Young
 
AgHntr10's Avatar
 
Join Date: Oct 2006
Location: Shepherd
Hunt In: Where the thieves and poachers roam
Default

Quote:
Originally Posted by Low Fence View Post
I hope whoever mandated them is one day put on a respirator... thatís plugged into one. I despise them


yes!
AgHntr10 is offline   Reply With Quote Back To The Top
Old 04-17-2018, 06:32 AM   #15
WTucker
Six Point
 
WTucker's Avatar
 
Join Date: Aug 2016
Location: Orangefield
Hunt In: Hardin County
Default

To answer your questions:

1- Yes they are required on new builds.
2- The latest code cycle requires AFCI basically everywhere but your garage, bathrooms, and outdoor circuits.

Depending on where you live, the authority having jurisdiction may still be using an older code cycle. This could change the requirements a little.
WTucker is offline   Reply With Quote Back To The Top
Old 04-17-2018, 07:15 AM   #16
Texastaxi
Pope & Young
 
Texastaxi's Avatar
 
Join Date: Oct 2006
Location: West of Houston
Hunt In: now accepting invitations!
Default

Quote:
Originally Posted by WTucker View Post
To answer your questions:

1- Yes they are required on new builds.
2- The latest code cycle requires AFCI basically everywhere but your garage, bathrooms, and outdoor circuits.

Depending on where you live, the authority having jurisdiction may still be using an older code cycle. This could change the requirements a little.
Which require GFCI ... which are almost as bad.
Texastaxi is offline   Reply With Quote Back To The Top
Old 04-17-2018, 07:25 AM   #17
TxKronik
Ten Point
 
TxKronik's Avatar
 
Join Date: Jan 2010
Location: Northern Bexar county/Bulverde area
Hunt In: Webb and Comal County
Default

They are also required in the 2014, 2011, and 2008 NEC may even befor that

When the state adopts the code it trumps local municipalities ordinances if they adopted an older code. Municipal (and trec) inspectors should be inspecting based on what is the newest code adopted either state or city.

The state is still on like the 2006 IBC so local municipalities can adopt any code cycle newer than that for the IBC (basically can be more strict not less)

That's why when the state adopted the 2015 IECC (Energy Code) everyone now has to do blower door tests and all the other dump stuff it requires regardless of what your city has adopted.

kronik by Diamond
TxKronik is offline   Reply With Quote Back To The Top
Old 04-17-2018, 07:46 AM   #18
TEX_hunt_AS
Ten Point
 
TEX_hunt_AS's Avatar
 
Join Date: Sep 2008
Location: Mansfield
Hunt In: Nowhere until I find a lease
Default

Wifes hairdryer tripped one almost every morning until we changed it to a normal breaker.
TEX_hunt_AS is offline   Reply With Quote Back To The Top
Old 04-17-2018, 07:52 AM   #19
TexasBob
Ten Point
 
TexasBob's Avatar
 
Join Date: Feb 2009
Location: NW Houston Area
Default

Inspector told us we passed because we had them when we bought the house. Then said to swap them out and save them until we sell. I haven't yet, hasn't been an issue for us yet.

Last edited by TexasBob; 04-17-2018 at 08:43 AM.
TexasBob is offline   Reply With Quote Back To The Top
Old 04-17-2018, 08:17 AM   #20
meltingfeather
Ten Point
 
Join Date: Oct 2012
Location: austin
Hunt In: Gillespie, San Saba & Kerr primarily
Default

Quote:
Originally Posted by jrfan View Post
They can be a pain in the butt like smoke alarms until you need them to save your house or your life. Then they are the greatest thing since sliced bread.
lol like that's ever happened
meltingfeather is offline   Reply With Quote Back To The Top
Old 04-17-2018, 08:36 AM   #21
Tony Pic
Ten Point
 
Tony Pic's Avatar
 
Join Date: Feb 2013
Location: NYS and Texas
Hunt In: NYS, Kerrville, Mountain Home and Harper
Default

Quote:
Originally Posted by TEX_hunt_AS View Post
Wifes hairdryer tripped one almost every morning until we changed it to a normal breaker.
Then the breaker did its job. Was the Mrs. plugging in the hair dryer with it on?
That would cause an Arc at the device and the breaker did its job.
I totally agree about the arc faults being a PITA. But if you stay in the scope of the breakers operation...they work fine.
GFCIs work good. Again, Only if you have a wiring problem( shared neutrals on gfci ckts ect) or turning stuff on, with it on, problem...These devices work fine.
Tony Pic is offline   Reply With Quote Back To The Top
Old 04-17-2018, 08:49 AM   #22
TEX_hunt_AS
Ten Point
 
TEX_hunt_AS's Avatar
 
Join Date: Sep 2008
Location: Mansfield
Hunt In: Nowhere until I find a lease
Default

Quote:
Originally Posted by Tony Pic View Post
Then the breaker did its job. Was the Mrs. plugging in the hair dryer with it on?
That would cause an Arc at the device and the breaker did its job.
I totally agree about the arc faults being a PITA. But if you stay in the scope of the breakers operation...they work fine.
GFCIs work good. Again, Only if you have a wiring problem( shared neutrals on gfci ckts ect) or turning stuff on, with it on, problem...These devices work fine.
First question I asked as well and she wasn't. I think the problem was the number of fixtures on that circuit (Plug, Lights, Vent Fan, Etc.) A GFCI is more convenient to reset, so that is the route we went.
TEX_hunt_AS is offline   Reply With Quote Back To The Top
Old 04-17-2018, 09:50 AM   #23
FLASH_OUTDOORS
Ten Point
 
FLASH_OUTDOORS's Avatar
 
Join Date: Aug 2012
Location: Tomball
Hunt In: Kennard
Default

Quote:
Originally Posted by Low Fence View Post
I hope whoever mandated them is one day put on a respirator... thatís plugged into one. I despise them


Iím still laughing at this.


Sent from my iPhone using Tapatalk
FLASH_OUTDOORS is offline   Reply With Quote Back To The Top
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 01:54 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2018, vBulletin Solutions Inc.
Copyright 1999-2012, TexasBowhunter.com