Default Bathroom Exhaust Fan

I recently installed 2 exhaust fans in my guest and master bathroom. I am having an issue with venting them to the outside of my house. I know better than just letting them vent into the attic. They are quiet as a church mouse when not hooked up.

The noise when I do hook them to the exhaust was borderline obnoxious. Granted, yes, I just stretched 25 feet of the foil tubing, and had it laying on top of the blown insulation, but couldn't stand the noise, so the project was put in "I'll finish it later" status. I'm guessing the little fan was working its tail off, trying to push that air through the flexible pipe.

I have reservations about drilling a hole in my roof, and installing a vent there, but it is a much shorter run of pipe to get to the outside, and probably a lot quieter. Also, I have a bathroom on the front of my house, so the vent would be clearly visible. Pic attached of the roof vent.

Any suggestions? I have watched the videos on This Old House a few times.

Thanks in advance.
Attached Images
 
hog_down is online now   Reply With Quote Back To The Top
Old 03-20-2019, 12:49 PM   #2
duckmanep
Ten Point
 
duckmanep's Avatar
 
Join Date: Oct 2012
Location: Northeast TX
Default

are we trying to get rid of moisture/steam from bathing or some funky bathroom odors? In my guest BR where I'm only getting rid of the stank, I vented to attic years ago and have never had a problem.
duckmanep is offline   Reply With Quote Back To The Top
Old 03-20-2019, 01:10 PM   #3
hog_down
Ten Point
 
Join Date: Mar 2017
Location: Houston, TX
Default

Moisture and funky odors, mainly.
hog_down is online now   Reply With Quote Back To The Top
Old 03-20-2019, 01:17 PM   #4
CabezaBlanca
Ten Point
 
CabezaBlanca's Avatar
 
Join Date: Oct 2015
Location: Rock Island, TX
Hunt In: Colorado County
Default

Attic.
CabezaBlanca is online now   Reply With Quote Back To The Top
Old 03-20-2019, 01:20 PM   #5
txhunter007
Ten Point
 
Join Date: Jan 2017
Location: Houston
Hunt In: Motley County
Default

Why not vent into the attic?
txhunter007 is offline   Reply With Quote Back To The Top
Old 03-20-2019, 01:21 PM   #6
the marshall
Eight Point
 
Join Date: Oct 2014
Location: Tomball
Hunt In: Tex-ok-la
Default

phart fans vent to attic
the marshall is offline   Reply With Quote Back To The Top
Old 03-20-2019, 01:45 PM   #7
bowhntrmatt
Pope & Young
 
bowhntrmatt's Avatar
 
Join Date: Dec 2009
Location: Stockdale
Hunt In: Concho, Val Verde
Default

Those fans are intended for humidity removal, and should be vented to the outside. Only way I would vent one into attic is if it was in a 1/2 bath with only a toilet/sink. Pumping humidity into your attic can be a very bad thing under the right (wrong) climate conditions.

As far as mounting the roof vent, as long as you have a composite roof with plywood decking it is really quite easy.
bowhntrmatt is offline   Reply With Quote Back To The Top
Old 03-20-2019, 01:47 PM   #8
tx_basser
Four Point
 
Join Date: Oct 2009
Location: Sachse, TX
Hunt In: Any place Public
Default

Never seen a house with fart fans vented to outside....
tx_basser is offline   Reply With Quote Back To The Top
Old 03-20-2019, 01:47 PM   #9
hog_down
Ten Point
 
Join Date: Mar 2017
Location: Houston, TX
Default

I'm not going to vent it into the attic, don't need any moisture up there. Trying to determine which would be easier, through the roof or out the side.

Thank you for your response, Matt.
hog_down is online now   Reply With Quote Back To The Top
Old 03-20-2019, 01:50 PM   #10
xman59
Pope & Young
 
Join Date: Mar 2009
Default

Quote:
Originally Posted by hog_down View Post
I'm not going to vent it into the attic, don't need any moisture up there. Trying to determine which would be easier, through the roof or out the side.

Thank you for your response, Matt.
going to be real hard to vent through a wall without tearing a junk of it out, then rebuilding it,,, venting through the roof will be much easier and is not hard to do
xman59 is online now   Reply With Quote Back To The Top
Old 03-20-2019, 01:51 PM   #11
bowtecmike
Ten Point
 
bowtecmike's Avatar
 
Join Date: Jun 2009
Location: Shallowater,tx
Hunt In: Kent County, SA St Park
Default

If you could get to the soffit I would go there, rather than cut through roof

Sent from my VS987 using Tapatalk
bowtecmike is offline   Reply With Quote Back To The Top
Old 03-20-2019, 02:04 PM   #12
sendit
Ten Point
 
sendit's Avatar
 
Join Date: May 2016
Default

Quote:
Originally Posted by bowhntrmatt View Post
Those fans are intended for humidity removal, and should be vented to the outside. Only way I would vent one into attic is if it was in a 1/2 bath with only a toilet/sink. Pumping humidity into your attic can be a very bad thing under the right (wrong) climate conditions.

As far as mounting the roof vent, as long as you have a composite roof with plywood decking it is really quite easy.
X2 agree with this. Keep the run as short and straight as possible, the less turns the better. These fans are not that strong and even using the flex tube hurts the air flow over smooth vent pipe.
sendit is offline   Reply With Quote Back To The Top
Old 03-20-2019, 02:25 PM   #13
elliscountyhog
Pope & Young
 
elliscountyhog's Avatar
 
Join Date: Jan 2008
Location: Ennis,Tx
Hunt In: WG Outdoors on Facebook
Default

Quote:
Originally Posted by bowhntrmatt View Post
Those fans are intended for humidity removal, and should be vented to the outside. Only way I would vent one into attic is if it was in a 1/2 bath with only a toilet/sink. Pumping humidity into your attic can be a very bad thing under the right (wrong) climate conditions.

As far as mounting the roof vent, as long as you have a composite roof with plywood decking it is really quite easy.
Yup! Code also requires it to the outside unless an operable window is present and even then some cities require it anyway. We try to go to the eve of the house if not too far away. If out the roof is closer we go there.
elliscountyhog is offline   Reply With Quote Back To The Top
Old 03-20-2019, 02:27 PM   #14
Tubby
Pope & Young
 
Tubby's Avatar
 
Join Date: Oct 2008
Location: Noonday, TX. ✞ CM ✞ ✞Jaspro✞ ✞ Rsatt ✞
Hunt In: Sterling County & The Diamond C!
Default

Quote:
Originally Posted by tx_basser View Post
Never seen a house with fart fans vented to outside....
Mine do...
Tubby is offline   Reply With Quote Back To The Top
Old 03-20-2019, 02:38 PM   #15
SaintBlaise
Four Point
 
SaintBlaise's Avatar
 
Join Date: Jan 2018
Location: New Orleans
Hunt In: Rocksprings, TX
Default

Quote:
Originally Posted by elliscountyhog View Post
Yup! Code also requires it to the outside unless an operable window is present and even then some cities require it anyway. We try to go to the eve of the house if not too far away. If out the roof is closer we go there.
Yep, it's code. Code enforcement knows best. So, vent it to the attic.
SaintBlaise is offline   Reply With Quote Back To The Top
Old 03-20-2019, 02:44 PM   #16
JHT
Pope & Young
 
Join Date: Oct 2007
Location: Houston
Default

Quote:
Originally Posted by hog_down View Post
Moisture and funky odors, mainly.

Changing your diet might be an easier option.
JHT is offline   Reply With Quote Back To The Top
Old 03-20-2019, 02:46 PM   #17
jlp04c
Six Point
 
jlp04c's Avatar
 
Join Date: Aug 2016
Default

I need to install one of these in my bathroom to remove moisture.. I was thinking I would just go out the side of my house vs up through the attic/roof...whats the consensus, is that a appropriate application?
jlp04c is offline   Reply With Quote Back To The Top
Old 03-20-2019, 02:47 PM   #18
Dale Moser
Pope & Young
 
Dale Moser's Avatar
 
Join Date: Oct 2006
Location: Wise Cty
Hunt In: Young Cty
Default

Quote:
Originally Posted by SaintBlaise View Post
Yep, it's code. Code enforcement knows best. So, vent it to the attic.
Do WHAT??? You must not deal with code enforcement much.. I know you're joking, but don't even type that!

I'd vent it to the attic.
Dale Moser is offline   Reply With Quote Back To The Top
Old 03-20-2019, 02:48 PM   #19
mfarmer
Ten Point
 
mfarmer's Avatar
 
Join Date: Oct 2011
Location: Port Lavaca
Hunt In: San Saba
Default

vent to soffit
mfarmer is offline   Reply With Quote Back To The Top
Old 03-20-2019, 03:15 PM   #20
elliscountyhog
Pope & Young
 
elliscountyhog's Avatar
 
Join Date: Jan 2008
Location: Ennis,Tx
Hunt In: WG Outdoors on Facebook
Default

Quote:
Originally Posted by jlp04c View Post
I need to install one of these in my bathroom to remove moisture.. I was thinking I would just go out the side of my house vs up through the attic/roof...whats the consensus, is that a appropriate application?
If the eve is closer then go there to the vent of the eve. If the roof deck is closer and wood decking go there. Shortest-straightest run possible.
elliscountyhog is offline   Reply With Quote Back To The Top
Old 03-20-2019, 03:17 PM   #21
CabezaBlanca
Ten Point
 
CabezaBlanca's Avatar
 
Join Date: Oct 2015
Location: Rock Island, TX
Hunt In: Colorado County
Default

Do you have soffit / ridge vents on your house? You'll get more humidity through those than you ever will through a fart fan.
CabezaBlanca is online now   Reply With Quote Back To The Top
Old 03-20-2019, 03:27 PM   #22
duckmanep
Ten Point
 
duckmanep's Avatar
 
Join Date: Oct 2012
Location: Northeast TX
Default

Quote:
Originally Posted by CabezaBlanca View Post
Do you have soffit / ridge vents on your house? You'll get more humidity through those than you ever will through a fart fan.
My thoughts as well

Sent from my SM-G930V using Tapatalk
duckmanep is offline   Reply With Quote Back To The Top
Old 03-20-2019, 03:36 PM   #23
mchunter67
Four Point
 
mchunter67's Avatar
 
Join Date: Oct 2012
Location: McGregor Tx
Hunt In: Ogelsby Tx
Default

All exhausting fan in a home should be vented to the outside. All new homes are built this way per ASHREA 62-2-16 code. If you have an existing fan or add a fan to a bathroom or kitchen vent to the outside you do not want moisture in your attic. I am in the business of building science an energy efficiency of a home just my 2 cents
mchunter67 is offline   Reply With Quote Back To The Top
Old 03-20-2019, 03:47 PM   #24
tdwinklr
Ten Point
 
tdwinklr's Avatar
 
Join Date: Sep 2017
Location: Leonard, TX
Hunt In: N. Central and N. East TX
Default

I vented both mine to the attic but ran the duct so that it would vent out the attic turbines. Seems good enough to me.
tdwinklr is offline   Reply With Quote Back To The Top
Old 03-20-2019, 03:53 PM   #25
JayB
Ten Point
 
JayB's Avatar
 
Join Date: Oct 2006
Location: Rowlett
Hunt In: Cass County
Default

Quote:
Originally Posted by mchunter67 View Post
All exhausting fan in a home should be vented to the outside. All new homes are built this way per ASHREA 62-2-16 code. If you have an existing fan or add a fan to a bathroom or kitchen vent to the outside you do not want moisture in your attic. I am in the business of building science an energy efficiency of a home just my 2 cents
Should listen to him ^^^

Mine are all vented to the attic.
JayB is offline   Reply With Quote Back To The Top
Old 03-20-2019, 08:17 PM   #26
CabezaBlanca
Ten Point
 
CabezaBlanca's Avatar
 
Join Date: Oct 2015
Location: Rock Island, TX
Hunt In: Colorado County
Default

Wet farts are worse than dry farts so you have to take that into consideration as well when trying to disperse any humidity/odors.
CabezaBlanca is online now   Reply With Quote Back To The Top
Old 03-20-2019, 09:10 PM   #27
bowhntrmatt
Pope & Young
 
bowhntrmatt's Avatar
 
Join Date: Dec 2009
Location: Stockdale
Hunt In: Concho, Val Verde
Default

I have 5 total in my house. All are vented to soffit.
bowhntrmatt is offline   Reply With Quote Back To The Top
Old 03-20-2019, 09:15 PM   #28
flywise
Pope & Young
 
flywise's Avatar
 
Join Date: Oct 2006
Location: Kempner,Tx
Hunt In: Blanco, Nacadoches,NewMexico,Colorado
Default

Your attic is or should be very well vented. There would be no problem just letting it go in the attic.
Now, I have seen dryer vents terminate in the attic and that's not good.
flywise is offline   Reply With Quote Back To The Top
Old 03-20-2019, 09:19 PM   #29
wfontjr
Spike
 
Join Date: Feb 2010
Default

Only if it was real cold would you get condensation in the attic, which is not often around orange anyway. Most of the time the attic is hot and can absorb more moisture into the vapor.
wfontjr is offline   Reply With Quote Back To The Top
Old 03-20-2019, 09:25 PM   #30
coachk
Associate Sponsor
 
coachk's Avatar
 
Join Date: Dec 2014
Location: Henrietta, TX
Hunt In: Clay Co
Default

I vented mine out the soffit... barely noticeable unless you're right under it

Sent from my SM-G930V using Tapatalk
coachk is offline   Reply With Quote Back To The Top
Old 03-20-2019, 09:51 PM   #31
Hawkpuppy 1
Associate Sponsor
 
Hawkpuppy 1's Avatar
 
Join Date: Oct 2009
Location: Waco
Hunt In: Texas
Default

Both of ours are vented outside and come out in vent screens under the soffit. Looks like basically 2" pvc pipe that the exhaust runs through.
Hawkpuppy 1 is offline   Reply With Quote Back To The Top
Old 03-20-2019, 10:13 PM   #32
bowhntrmatt
Pope & Young
 
bowhntrmatt's Avatar
 
Join Date: Dec 2009
Location: Stockdale
Hunt In: Concho, Val Verde
Default

Quote:
Originally Posted by flywise View Post
Your attic is or should be very well vented. There would be no problem just letting it go in the attic.
Now, I have seen dryer vents terminate in the attic and that's not good.
Take a shower in the winter with your exhaust fan running. Vent that heated, humid air into the attic and you will literally have rain falling off your roof decking. Dryer vents are just as bad and have other issues on top of that.
bowhntrmatt is offline   Reply With Quote Back To The Top
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:39 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2019, vBulletin Solutions Inc.
Copyright 1999-2012, TexasBowhunter.com